Is this Schneider SCADAPack 330E recoverable?

ajmist

Member
Join Date
Jun 2014
Location
Tucson
Posts
6
Hi People,
I have a ScadaPack 330E that has been sitting on a shelf for a few years (previously working), and have recently re-installed Schneider's SCADAPack E Configurator (and Workbench) to a new windows 10 laptop.
When trying a USB connection (Refresh button from Controller Status page), I'm getting a modal dialog box error :
"Request: Page Read Request"
"Status: DNP Status: Function code not supported (IIN bits set)
The configuration diagnostics then have a few messages (pasted below).
I've tried "Cold Boot Mode" and "Factory Boot Mode" (holding down the config button for varying times on boot) without any improvement. Any ideas?

<+++ Master 32000 Build DNP3 Message: Table Read
<+++ Master 32000 Insert request in queue: Table Read
<=== Master 32000 Application Header, Read Request
FIR(1) FIN(1) CON(0) UNS(0) SEQ# 4
===> Master 32000 Application Header, Response
FIR(1) FIN(1) CON(0) UNS(0) SEQ# 4
+++> Master 32000 Process response to request: Table Read
===> Master 32000 IIN Bits:
IIN1.6 Device Trouble
IIN2.5 Configuration Corrupt
IIN2.0 Function Code Not Implemented
 
Seems like the device is actually replying, as you're getting the IIN trouble flags back.

Factory Boot normally just sets the comms parameters back to default so you can talk to the device if you don't know the comms port setup.

I would try creating a basic config with everything set to default, and see if you can write that to the unit. If you're lucky that will fix the corrupt configuration.
 
Agreed, yes the device is communicating - even flashes leds when I send it something on a serial port instead of usb.

Sadly it appears there is some handshaking, so going direct to a download didn't work on serial or usb.


I've taken it up with Schneider support.
 
The issue was resolved by a more recent SCADAPack E Configurator (the download / configuration software) supplied by Schneider.


It appears the SCADAPack Firmware was too new for the older loader software.
 
Thanks for the feedback, had not even thought of that as a possible issue. I've only got one E series left (rest are 474 or 574s).
 

Similar Topics

SCADAPack 330E has various ports and protocols available. I'm using Modbus RTU over serial. I/O Devices (scan packets) configured for this have...
Replies
2
Views
1,972
hi to all, have anyone tried to communicate Schneider PM800 to a ML1400 through rs485? i am having an issue with it just receiving message...
Replies
1
Views
51
Hello All, I am stumped on how to convert a %MW to a %MF using Machine Expert Basic and a Modicon M221. The help files show a word to a double...
Replies
4
Views
177
Hi, Is Control Expert V15.0 supposed to support multiple monitors? I'm running Control Expert V15.0 on my host Windows 11 PC, connected to two...
Replies
1
Views
91
Everything was working fine, but suddenly CPU went into error mode, and the ERR and TER LEDs lit up. Now I can't download or connect with the PLC...
Replies
0
Views
107
Back
Top Bottom