Dear,

i want to understand something...
i hae a specification here that says that pressure transmitter loop powered, 4 to 20mA HART output, load driving capability of 600 ohm at 24 VDC.

what is the load driving capability?
 
That is more often referred to as max load, or max resistance, or max burden. It simply means that with the 24 VDC power supplied the transmitter will enable it to send a 4-20 mA signal through a circuit with a total resistance of 600 Ohms. That allows, for example, putting a chart recorder with 250 Ohms resistance and a PLC with 250 Ohms resistance on the input channel in the loop and the transmitter will be able to drive the signal through the loop.

If you exceed the max load for the transmitter your output signal will typically drop to zero mA.
 
Sensor Imipedance and effect on Input module

Dear Tom,

thank you! i was looking at the endress&hausser Promag 53 datasheet, please check below:

[FONT=E+HWeidemannCom-BookBd][FONT=E+HWeidemannCom-BookBd]
"Promag 53​
[/FONT]
[/FONT][FONT=E+HWeidemannCom-Book][FONT=E+HWeidemannCom-Book]
Current output:
active/passive selectable, galvanically isolated, time constant selectable (0.01...100 s),
full scale value selectable, temperature coefficient: typically 0.005% o.r./°C (o.r. = of reading),
resolution: 0.5​
[/FONT]​
[/FONT]μ[FONT=E+HWeidemannCom-Book][FONT=E+HWeidemannCom-Book]A
• active: 0/4…20 mA, R
[/FONT]
[/FONT][FONT=E+HWeidemannCom-Book][FONT=E+HWeidemannCom-Book]L [/FONT][/FONT][FONT=E+HWeidemannCom-Book][FONT=E+HWeidemannCom-Book]< 700 [/FONT][/FONT]Ω [FONT=E+HWeidemannCom-Book][FONT=E+HWeidemannCom-Book](HART: R[/FONT][/FONT][FONT=E+HWeidemannCom-Book][FONT=E+HWeidemannCom-Book]L [/FONT][/FONT][FONT=E+HWeidemannCom-Book][FONT=E+HWeidemannCom-Book]250 [/FONT][/FONT]Ω[FONT=E+HWeidemannCom-Book][FONT=E+HWeidemannCom-Book])

• passive: 4…20 mA, operating voltage V
[/FONT]
[/FONT][FONT=E+HWeidemannCom-Book][FONT=E+HWeidemannCom-Book]S [/FONT][/FONT][FONT=E+HWeidemannCom-Book][FONT=E+HWeidemannCom-Book]18...30 V DC, R[/FONT][/FONT][FONT=E+HWeidemannCom-Book][FONT=E+HWeidemannCom-Book]i [/FONT][/FONT][FONT=E+HWeidemannCom-Book][FONT=E+HWeidemannCom-Book]150 [/FONT][/FONT]Ω"

I assume active is field powered and passive loop powered.

What is Ri? RL is the load resistance as you explained before.
and why RL for HART should be larger than 250 ohm?

what are the restriction on the input module resistance?

thanks!

Charbel

 
Hart requires a resistance > 250 Ohm in order to have enough voltage to make the communicaitons signal readable by Hart devices. Remember, Hart is a high frequency communications signal superimposed on top of the 4-20 mA.


I am not sure about the Ri. I could speculate, but i suggest you contact your source for E & H or their tech support.
 

Similar Topics

When i load my client a[plication the following error is recorded in factorytalk view studio log Failed to load data server...
Replies
0
Views
59
Background for the question: A service man from a sub-supplier has made changes onsite to a Siemens PLC and HMI program. He has not made a backup...
Replies
7
Views
301
I have a 90/30 CPU331. I am trying to upload the program out of the CPU and keep getting an error uploading the logic. Error 8262: Error...
Replies
6
Views
129
I am connecting to a remote device. When attempting to upload I receive an error that states: Error: Auto_Functions: The Import was aborted due...
Replies
3
Views
204
Good people of PLCs.net, I am currently working with an HMI that is advantech 1250H, that communicates with a 1769 Compact logix and Currently...
Replies
2
Views
100
Back
Top Bottom