I have an application where I have a micrologix 1100 configured as a modbus RTU master, connected by an 1763-NC01 to a network of Telemecanique Tesys U motor starters. The majority of the time the communications performs very well but once every couple of months Channel 0 on the controller seems to lockup, Comms stops and will not restart unless i power cycle the PLC. It isnt any of the slaves that are causing the issue because i do not have to power cycle these.
Is there any way to unlock / reset the comms port without the customer having to power cycle the plc?
I assume you are getting a 37H error code on your MSG instruction when this is happening? The short answer is no, the buffers are filling up and the only way to reset them is a power cycle or download.
Previously we have had the same problem when communicating to multiple modbus devices (a single device does not seem to exhibit the same problems) with the 1100 but i found the lates firmware to be alot more stable. You can download it from here
http://www.ab.com/programmablecontrol/plc/micrologix1100/downloads.html
Hi, I cannot find the DLCA1764.EXE utilty software for data retrieving. Can someone share the link to download this software. Thanks!
158
I am currently backing a Micro Logix 1100 and no-one seems to have the file for me to upload from. Is there a way for me to upload the project off...
560
I am trying to set up a read message in a MicroLogix1100 to read the value of a DINT in a ControlLogix5561. I have successfully set up a message...
206
Hello, I have an existing application that has a Powerflex 700 with a 20-COMM-E adapter controlled by a Micrologix 1100 via Ethernet. The setup...
1,206
I have a MicroLogix 1100 and it's capable of ac or dc output voltages. What I don't know is how I'm supposed to tell the 1100 to use dc for the...
1,439