MicroLogix 1400 (math based?) programming question
Skidood
Oct 2016
Ontario
219
Hi Group,
I'm the new owner of an AB MicroLogix 1400 processor and have been trying to decide the best way to de-pressurize a compressed air tank using a solenoid valve which releases some pressure.
I want to de-pressurize the tank at a rate of 0.8 psi per minute by energizing the valve as needed in short bursts.
Your wisdom would be greatly appreciated ! 🍺
Interesting project, the big picture is to compartmentalize your logic:
A more suitable valve for the application would be an actuated control-valve, but you know that already.
If all you can do is open/close then I would try:
- Make logic to pulse the solenoid based on Rate.
- Use PID or roll your own logic to control the Rate
I should have said the de-pressurization rate cannot be faster than 0.8 psi per minute or slower than 0.4 psi per minute.
And the tank has an inherent bleed-down rate of its own outside of external control of approx. 0.2 psi per minute.
let me ask this: how can I configure ladder logic to pulse an output, say for example, once every 20 seconds for a duration of 1.5 seconds.
If I can figure this out, I can set up 5 or 6 rungs where each one starts with a LIM instruction (using the pressure reading) and each rung is responsible for a certain portion of the pressure decay (say the portion between 7 psi and 4 psi.
Two timers?
Set up a timer with a twenty second preset. Have the timer's "Done" bit reset it. Use a "Less Than" instruction to compare the timer's accumulated value to 1.5 seconds and turn on the output when the "Less Than" instruction is true.
Thanks Steve, your a star.......that's the kinda trick I was looking for. I am not too experienced with programming a PLC but I am definitely getting hooked.
hi to all, have anyone tried to communicate Schneider PM800 to a ML1400 through rs485? i am having an issue with it just receiving message...
42
105
137
Hi, I am working with a Micrologix 1400 model 1766-L32BXB. With no input wires connected to the “in12” thru “in19”, I am getting 24 volts while...
254
Hi everyone, I hope I don't butcher this up, please feel free to critique me wherever if I do, I have an issue I would equate to "chasing...
357