hi all, good day to you...
im new with plc program,
and im facing some problem...
im using gx-work 2 (simple project type) , Q00cpu
1st- how should i create a ladder for time , date (according to real time) ?
- switching on every 8am - 11pm? switching off every 11.00pm -8am?
2nd-i have a input module (aj65sbt-64ad) on station 3, connect to 2 diffrent pressure transmitter.(4-20mA)
i want to get the averange of the pressure and control the (VSD).
Any advice on functions to use would be greatly appreciated 🤞🏻🤞🏻
Alvis
Hi Alvis,
You can read the time in the systemregisters SD210, SD211 and SD212 and the SD213
SD210 = Year and month
SD211 = hour and day of month
SD212 = minute and sec
SD213 = Year (higer digits) and day og week
The data is read in BCD in hex.
Ex. SD210 = H1403 = Year xx14 and march month
lowbyte = month
highbyte = year
Use SD213 gives you the higher digits of year ex. 20xx
For your application you need to read the SD211 and make a compare in your logic.
For your second question.
The module seems to be a CC-Link slavenode.
If you have used the settings in "Parameter" -> "Network Parameter" -> "CC-Link" the you read the actual (raw) walue in the dataregister typed in.
Find the area of dataregister for slave 3 and make a calc to output to your VDF'S
btw, are they connected on the CC-Link og hardwire with an analouge output?
Maybe you shoul list up your configuration of the PLC.
Best regards
Dariusch
hello Dariusch,
thanks so much for replying me=)
they connect via cc-link,
64ad is at station-3
vfd at station-5.
isit every station occupied 4 dataregister?
if my I/O assignment start from
X100 , Y100
(Rwr)-D100 , (Rww)-D200
which means station-3 is (Rwr)d108 /Rww(d208)
ld x21b , ld x200 , mov d108 d300 ? ( pressure of transmitter chn-1?)
ld x201 , mov d109 d301 ? ( pressure of transmitter chn-2?)
sm400 , + d300 d301 d302
sm400 , / d302 k2 d303
ldi x19d , mov d303 d216 ? ( x19d =VSD Frequency setting command )
set y19d
then the frequency will follow the d303?
or i need to convert the d303 to frequency?
but u did mention that ( make a calc to output to your VDF'S)
how i suppose the write into there?
im very confuse.
thx for helping me , guys. 🤞🏻🤞🏻
Hi Alvis,
I need you to make a screendump like my, so I can se your configuration of the CC-Link.
Each CC-Link device can consists of 1 to 4 stations, depending of the device.
Each station has 32 bits r/w and 4 words r/w. So 32 input, 32 output bits e.g. M0 to M31 (Read), M100 to M131 (Write) and 4 indput words and 4 output words e.g. D0-D3 (read) and D100-D103 (Write).
The 64ad shoul be configuratet as a "Remote I/O Station" and consists of 32points.
The VFD shoul be configuratet as a "Remote Device Station" and consists of 32points (32 I/O bits and 4 I/O words).
What kind of VFD do you have? I have a FB for the Mitsu's with the "FR-A7NC" option card.
/Dariusch
set y19d
according to this ladder,
(64-ad) channel 1 + channel 2 then divide by 2 = averange
vsd only will run averange speed....
if when pressure dropping down....
i would like to ramp up the vsd speed... how i suppose to do it?
Hi Alvis,
First here is a link for the FB to the FR-A7NC module.
I have not used this in a GX-Works, only in IEC, but should be the same.
http://www.beijer.dk/web/web_dk_be_dk.nsf/docsbycodename/filearchive?OpenDocument&mylink=/web/BexFilePileAUT.nsf/fm.be.searchframe?Openform&Lang=DK&DocID=CEF8F746FCAAC290C12579B200411E97
The I/O configuration of your system should be like this
Station 1 = X100-X11F, Y100-Y11F, D100-D103, D200-D203
Station 2 = X120-X13F, Y120-Y13F, D104-D107, D204-D207
Station 3 = X140-X15F, Y140-Y15F, D108-D111, D208-D211
Station 4 = X160-X17F, Y160-Y17F, D112-D115, D212-D215
Station 5 = X180-X19F, Y180-Y19F, D116-D119, D216-D219
/Dariusch
I guessing that you want to keep a konstant pressure?
If so, just use a simple PID, also there are FB for that to, and use the D303 as the PV-value, the output will be D216 (VFD). You now only need the SP-value??
/Dariusch
/Dariusch
Sry Dariusch for my late late Reply...
Does your SP-Value meaning Single Pluse value?
Im using this as Stair Case Fan...
When somebody open stair case Door...The Pressure inside will drop down..
So the VFD need to Ramp Up , put more pressure into stair case.....
After I testing On Site.....I Can get the figure of 64ad..
but when i send it to VFD.....it remain on 30hz..
I dono why VFD dont have any respond.
Isit i need to write the Operation Mode CODE?
I am using Mitsubishi GXWorks 2 with a FX3U I must make additions to a program that is not documented very well. Is there a way to tell which...
1,970
Hello! If someone can help me with the following problem. I can't change the phone number. Do I really need the interface (AL-232CAB - Programming...
59
how to communicate FactoryTalk Optix and Mitsubishi Q Series. I want to know the details of that
56
HOW to communicate with OPTIX and Mitsubishi's Q Series PLC?? PLEASE HELP ME
64
I'm at a new job as the sole control engineer and trying to piece together where my predecessor left off. One machine I'm trying to get online...
113