I’m using a QJ71MB91 modbus card in a Mitsubishi Q series PLC. It’s being used as a slave, and everything’s working fine aside from the error light.
When I unplug the modbus connection (port 1) the error light sometimes comes on when I reconnect. It’s a genuine error being caused. When I open the system monitor in GX Works 2, I can view the modbus card status and there is a button to reset the error, which works ok and the error LED goes out.
What I’d like to do is the same error reset from the PLC code, that way it could be linked into a reset button on SCADA.
Anyone know if it’s possible, and how to do it?
Thanks for any pointers....
Hello:
I had a look at the manual and it seems all the system functions are reserved, both on the MELSEC backplane "Y" or discrete output signals and the buffer of shared memory between the Melsec Q and the QJ71MB91Modbus module. I found the manual in the below link:
https://dl.mitsubishielectric.com/dl/fa/document/manual/plc/sh080578eng/sh080578engj.pdf
However, there is one functionality that may help you, but I do not have this module to test my hypothesis, but here it is:
Using the ZP.UINI it seems to be possible to change some operation parameters. So I wonder if you change the operation parameters to something different than what you need, then again back to what you need, you could correct the error lights that you need to disable.
Hi Andy,
Is it possible you u share your modbus setting?
I got problem to set the parameter.
FYI, my CPU using is Q03UDVCPU, but my QJ71MB91 module set as master.
Please advice.
Bonjour, Je n'ai pas de communication modbus RTU vis la configuration ci-dessus. J'ai essayé les deux mode ch1 et ch2 mais rien ne fonctionne...
171
Hi hope all are ok. I have mitsubishi PLC Q03UDV CPU. I have control a drive through modbus inteligent module QJ71MT91 in GX Works2. Any experts...
619
Hello Anyone I have Stepper motor with control AZD KD and BLVD20KM ORIENTAL.I Want to communication with QJ71C24N modbus rtu Mitsubishi ,How...
1,173
I am trying to get a Mitsubishi GT2715 HMI to read and write from a Eurotherm 3508 controller using 4 Wire RS485 Mobus RTU communications. The...
1,310
How to program (Ladder) Modbus TCP on Mitsubishi FX5CPU using its Predefine Protocol Support Function
1,682