Modbus addressing Wago 750-8206
ccanedo
Apr 2016
Miami
I am using a Wago 750-8206 controller and a Magelis HMIGTO6310. I am trying to use modbus tcp comm between the 2 devices. Does anybody know the modbus addressing on the Wago PLC?
Thanks in advance
%I - From 0x000 -> 0x17ff
%Q - From 0x1800 -> 0x2fff
%M - From 0x3000 -> 0xffff
Note that you'll have to add 1 to all of these addresses to get the Modbus address. For example %MW0 would be 412289.
Good luck!
Yosi
%I would therefore start at 400001
%Q would therefore start at 406145
You can, of course, read all of the DI and DO from the PLC using their bit addresses %I would start at 100001 and %Q at 000001.
Cheers!
Hi Yosi,
I have tried all that and no luck.
I am using codesys e!RUNTIME. I have been told by a WAGO rep that the modbus addressing change from Codesys 2 to this new e!****PIT software.
Do you know anything about it?
Hi Yosi,
I used the same protocol before in a Wago 750-880 PLC and it worked. But I was using the old Wago Cosedys Software. Now I am using e!****PIT which use e!RUNTIME (codesys 3).
I am suing the Modbus Master Manager to modbus address my variables. For example, I have a WORD var that I choose to be a R/W register then e!****PIT automatically assigned 32000 to that variable.
Do you know what memory should I access and what address number should I use?
Also, an interesting fact. I tried to change the value of that variable in the PLC and defaults back to 0
Thanks in advance
Hello everyone. Using the designer software for the HC900 had me thinking. How can I assign 1 variable so 1 single bit. Like how can I say that...
449
Hi, I am doing PLC using M221 as a slave device and communication via modbus. The PLC has been completed and i am required to provide Modbus...
2,859
Hi All, I would like to know is there any option in Wecon pi studio for Modbus addressing. I have gone through the options but I can't find the...
1,181
Does anyone have a good doc that explains the addressing for modbus with unity. I am having issues setting up the addressing when trying to...
3,983
Hello everyone, I am working on a project that requires a connection to Alstom relays series P40x using Modbus RTU, and I am having trouble doing...
981