Modbus Communication
adam_lhadi
Feb 2022
algeria
59
Hi everyone
i have a delta VFD-M series with RS-485 protocol RJ-11 (Modbus communication) and cm1241 rs-485 siemens module (6ES7 241-1CH32-0XB0)
so i needed to transfer the DB9 connector to RJ-11 to establish the communication between the vfd and the plc
the picture shows how i managed do adapt the two connectors
please correct me if am wrong
kind regards
If DB9 pin 1 is truly signal ground, then yes, you have the correct connections.
I have seen other devices use pin 8 for A(-), pin 3 for B(+) and pin 5 for signal ground.
Be aware that some manufacturers define the A and B driver lines backwards so that A to A and B to B does not work.
If the driver lines are connected backwards, there's no damage, but communications will not work. The fix is to swap the lines on one end.
Apologies for not being the best IDEC programmer. I recently was doing some inspections on a site that had 3 FC6A IDEC processors. The issue is...
86
Hi all I need help on this As in my project used Schneider TM241 controller. Now I want to communicate Elite energy meter with controller by...
168
Hello, I need to access the bits from the fire system control panel through RS-485. So, I used Read Var block to read from the panel...
198
Hi, i cant establish communication between fatek plc with an energy meter, both capable for modbus tcp, i did with modscan but fatek plc does not...
151
Hi Guys, I am a new member and this is my first post! I have a little PLC experience but it is mostly with siemens logo and using ladder...
905