Modbus TCP/IP Communication
vinayakid
Dec 2007
PNQ
Happy New Year !
I am trying to establish the communication between Telemecanique PLC and AB ControlLogix PLC.
The Tele PLCs are on the Modbus TCP/IP network. I want data to and from these PLCs to the ControlLogix PLC.
The ControLogix is on a seperate EtherNet network. I can add a third party communication module to CLX chassis if requried. and also do the necessory cabling for that.
Can anybody suggest me a method to do this ?
Also note please let me know if the Modbus TCP/IP N/W can handle the string data transfer between Tele PLC and CLX PLC.
Thank You,
Vinayak
[email protected]
Prosoft technologies has the modules that will do what you want. They have a new one out, I don't remember the number, that does that translation for you without any configuration on your part. At least that's what Prosoft advertises.
Steve
Modbus does not have native support for strings. I have never worked with these specific PLCs, but unless you can access the string's memory directly, you will have to convert them to their ascii numerals, store them in integer registers, and send them as integers. Then on the other side you can move them back from ascii to characters.
I have done this using a Red Lion DataStation Plus product as the middle man between a Modicon PLC talking ModbusTCP and the ControlLogix PLC with the L5K file driver imported in to Red Lion Crimson software. It was so easy a Caveman could do it. I also share the love of the DSP to talk to a Yokogawa PLC at the same time as well to the AB PLC. Again, super easy and simple to do. Here are some photos:
DSP In Action
Joe_WaZoo
As jonnies points out, it may be that Vinayak did not literally mean a "string" but rather an array of integer data values. No matter what method is used, the data types should be better understood.
For Modbus or Modbus/TCP communications to a ControlLogix platform, I have always relied on ProSoft Technology.
The current slot-mounted product for ControlLogix is the "enhanced" module MVI56E-MNET.
I do not recommend devices that advertise EtherNet/IP functionality but have not undergone ODVA conformance testing.
DSP In Action
Joe_WaZoo
I have a similar application as Joe_Wazoo but i'm having problems importing the tags from the .L5k or the .CSV file.
When I try with the CSV file it tells "The following lines in the file contained erros: 1,2,3... The lines without errors where imported"
and when i try with the .L5K "You have made changes to the Logix Tag Names that may invalidate data tag references in the database. You should correct this by running validate all tags utility from the data tags window"
anyway, i can't import the tags.
thanks
That message you see after the .L5K import is fine--you just need to go to the 'Data Tags' tree and press the 'Validate All Tags' button.
I already tried that, but since I have no tags to validate, nothing happens.
I try to do it backwards, generate an .csv export file from the crimson, and try to import to the RSLogix, and it shows me a mismatch import export version.
The L5k import should populate your Communications Protocol - Native AB L5k tags. I think you still have to create the tags in you Data Tag area to use them on your application screens.
Hi folks, I have a Controllogix in communication with a zigbee coordinator using Logix AIO for modbus tcp. This zigbee coordinator have 3 slaves...
341
Hi, i cant establish communication between fatek plc with an energy meter, both capable for modbus tcp, i did with modscan but fatek plc does not...
183
can i send and recieve data using my yokogawa UT35A controller with my siemens s7 1200 plc using profinet communication without using gsd file
409
CR3000 HMI ModBus TCP/IP Master has gotten erratic after increasing block size to 24 at DA70A in Protocol 1. What should a practical guide be for...
583
Good day Programmers I have a RSTi-EP CPE100 Standalone Controller from Emerson as well as a STXMBE001 (MODBUS TCP/IP) as a Modbus communication...
662