MSO Allen Bradley
ELGC
Sep 2020
USA
19
Hello everyone, I hope you can help me. I have a VFD 527 this kind of VFD can be programmed with the motion commands like MSO, MSF, etc... Every time I am sending a MSO (Motion Servo On) the motor starts moving, How can I avoid that? I just wanted to send the MSO and the motor has to be stopped until I send the Jog.
Thank you in advance for your help.🍺
Does the motor run at a specific speed, or does it just "creep" at low speed ?
There is an RA Knowledgebase document (#QA54233, Access Level: Everyone) that describes low-speed motor "creep" after you enable the servo loop with an MSO on the PowerFlex 527 and 755.
https://rockwellautomation.custhelp.com/app/answers/answer_view/a_id/559540/loc/en_US
My understanding is that this only happens when the drive is set up for Volts/Hz operation (the least sophisticated operating mode), because the Slip Frequency setting causes the motor to spin trying to create torque. You can set Slip Hz = 0, or configure the drive for Sensorless Vector (or, of course, use a motor with an encoder) to resolve this issue.
Thanks you for your answer, the motor just creep at low speed. I am going to look for that parameter Slip Hz.
Best regards
Hi Ken,
I have already changed the Speed Slip Hz to 0 and it works. If I want to change the configuration of the drive to Sensorless Vector, What do I have to take into consideration? Also I am having trouble to stop the motor because the time it takes to stop at full speed is too large. Best Regards
The drive needs to know a little more about the motor in order to do Sensorless Vector mode, so as that Knowledgebase document says, you need to at least run the Motor Analyzer test.
I don't know anything about your application so I can't tell you if the motor and drive are sized correctly for its dynamics.
If you need to decelerate a heavy load using the motor only, your options are a drive with sufficient excess capacity on its own DC bus, or a dynamic brake resistor feature, or a drive that allows regeneration onto the AC mains (an active-front-end drive), or a DC Common Bus drive system.
Since you have already selected and installed the PowerFlex 527, the most likely option is to install a dynamic brake system. The PowerFlex 527 has a built-in braking transistor to bleed off power from the DC bus, so adding a resistor pack is literally a two-wire connection.
There is an Application Technique publication that can help you calculate the proper size of dynamic brake resistor for your duty cycle and load:
https://literature.rockwellautomation.com/idc/groups/literature/documents/at/pflex-at001_-en-p.pdf
Good morning, We've had an issue with a couple of servo valves and was wondering if anyone had seen anything similar. After a drop in pressure...
110
Have a system that has been running for over a year and all of a sudden getting a ExcessiveVelocityFault on one of the drives when the MSO command...
157
Hi guys, I have an issue I cannot solve by myself ... While commissioning, the E-STOP was pressed and now the servo is in half cycle with MSO...
491
Gentlemen, I have come across an issue which I can't understand. So I had to change the 35:1 gearbox with 25:1 gearbox. I did change the...
1,189
Hi, with my Kinetix 6500 axis system I have the very random problem that the MSO instruction fails with error code 22 "Stop the axis before you...
2,971