Can you cross reference to see if that output is used anywhere else in the program ?
Have you done a cross reference on the bits (highlight and right click > Cross Reference or press Ctrl+E) to see that they're not being set somewhere else in the program somehow?
Is this inside an AOI? If it's inside an AOI, have you clicked down to the specific instance using the dropdown menu in the top right of the screen? I'm guessing it's not an AOI because that dropdown isn't visible, but it also looks like Logix is running on a PanelView of some sort.
Is the routine that OTE is in being scanned? Can you toggle it off (Right click, Toggle Bit or CTRL-T)
Output should not be active
Yes the routine is being scanned and I am able to toggle it off. I toggled these bits off yesterday and attempted to run another cycle last night but these two OTE's reactivated and locked in again. I never reached the 100psi required for the fault OTE to ever activate even if the limit switch was not engaged.
they are the only OTE's in the program for these tags