output voltage
barak
May 2006
be'er sheva
i'm planning on using a plc with pnp digital outputs.
the plc uses 24VDC.
i need to operate a few solenoind valves of 24VDC.
will the plc provide them the 24VDC they need, or will i need another relay?
if the plc uses 24VDC, does it mean i can connect to it loads up to 24VDC?
The outputs are isolated. They have nothing to do with the PLC operating voltage. The outputs don't supply voltage. Treat them as relay contacts - contact closure.
If you want to use 24DC valves, connect the positive leg of another independent 24DC supply to the Common of the output module. When you turn on an output, the associated PNP transistor will turn on, and 'Supply' the positive leg of your supply to the solenoid.
Just make sure that the current demands of your solenoids do not exceed the MAX current limit for the particular PLC output.
PLC 24v DC output
Barak,
Be sure to fuse your outputs, if the PLC has no internal fuses for each output. Also, In my experience I have found that the isolated semiconductor outputs, as opposed to relay outputs are more sensitive to voltage transients. If a relay is powered on and the contacts of that relay energize the solenoid, it provides additional protection to your PNP output card. The relay output is not as susceptible to voltage transients, but then you have the 1 million physical make/break limitation (before the relay goes bad in the PLC) and the slight lag in time that actual physical contacts take to make/break.
Just a thought.
Mike
Hi Barak.
Check if the DC output can drive the solenoid (Amps).
A relay is a cheap insurance. It is cheaper to replace a relay than a whole PLC or an output card.
In any case, remember to install surge suppressors over the coils.
Freewheeling diode, or zener diode.
It is not the connection of the coil that will kill the output or the relay, it is the disconnection of the coil!
I have a Siemens 1515 controller with the configuration of cards (input, output, safety input, safety input, safety output). I am having an issue...
194
hello everyone. I have a 525 VFD that works, the screen shows the output voltage and the output frequency but in UVW I do not have voltage...
199
Pretty simple question, but I was wondering how I can set the Analog Output 1 of an S7-1200 (DC/DC/Relay) to be proportional to a data tag. I...
856
Hi; I need to monitor and log the 3phase AC input voltage for which I need a device to convert AC input voltage (say 350 - 440V) to analog (0-10v...
1,382
I am having with voltage on an issue with the automation direct productivity 3000 p3-08tas output card. The out out is wired to 120v, which is the...
3,685