Is there any chance to edit the caption text at runtime?
I need to create a list of editable captions of 5 characters.
I am using RSViewStudio ME 4.0
PanelView+ 600
ML1500 LRP
The only method I know is just to insert a string variable into caption ant to edit it. However the string variable is "only" 42 words.For now I can edit about 32-38 strings as after that I am out of memory on plc.
So is there any way to edit caption text at runtime and the text just to remain into PV+ memory?
Or any method to create smaller STring variables?
Thank You
Marian
Create "Memory Tags" in the RSView ME application itself and you can edit those just like you can String data table elements in the controller.
In the tag database, create a tag where the Tag type = String. Select the Type = Memory selection button and check the "Retentive" checkbox.
You can edit each one of these at runtime by making a String Input Enable object and making this String tag the caption.
Wow, this is really simple.
It is even in the manual :)
Always I am telling myself I should read the manual more thoroughly, not just to screen it, but.....
Thanks Ken
Marian
Hello all, First post here. Hitting a wall with finding info on this topic online, and none of my coworkers have a clue. I have a PanelView...
1,367
Hi all, i was serching unsuccessfully something relationed with this issue. I have a screen with several labels, some of them with the same "Y"...
2,713
I have a system using a Panelview Plus Standard (2711P-T10C21D8S). It is configured with 86 alarms, most of which work fine, but for about five...
2,269
The application looks fine in the test run at the development node(my computer), but when transfer to the Panel View I can see some of the labels...
4,766
I'm at a loss here and hoping someone else has seen this: Background: We've got two identical machines on our floor (we'll call them machine A &...
70