PanelView Screen directed by PLC
rmb550
Nov 2009
Ontario
86
I have been using PanelView T6 and T10 -- and want to use the 3" version in a lower cost application. I am wondering how one gets the HMI to jump to a certain screen based on some status in the PLC --- i.e. if I have an alarm in the PLC (defined by my program) I want the HMI to navigate to a specific screen where the alarms are listed. Note this is as defined by my program in the PLC and is not the "alarms" that are HMI - tag defined.
Thanks in advance.
RMB
If you are talking about stanadard Panelviews. Then see picture below.
Pay special attention to the last sentence, you must release control so a operator can change screens again.
Mickey,
Thanks for that -- but I am using the PanelView Component Operator Interface that has the built in design software, and does not use the PanelBuilder software. Any ideas?
RMB
I have not used this functionality with the PanelView Component, but I believe you should be able to control the HMI screen through a PLC tag if you go to: Tags / Global Connections / 19 - Current Screen Number (Read/Write). See attached screenshot.
You can also download the emulator software from Rockwell's site. This will allow you to edit a Component application without having a PanelView Component terminal.
http://www.ab.com/eoi/graphicterminals/downloads.html
I'm at a loss here and hoping someone else has seen this: Background: We've got two identical machines on our floor (we'll call them machine A &...
70
I'm working on a system with three Panelview 7's connected in a DLR. The system started having miscellaneous DLR faults and they were supposedly...
491
I'm doing my first PanelView 5000 application with Logix View Designer v8, and am of course jumping in headfirst. One thing I don't find is a way...
714
Howdy Everyone, We had to replace a panelview 600 2711-B6c20 the other day and when we did, the new one none of the screen selector buttons work...
1,134
I have 2 PV Plus 7 screens used in the same system that both have touch screens that can be challenging to activate after they haven't been...
591