PLC-2 Help

ramil

Guest
R
Dear All,
I am converting PLC-2 to PLC-5 and i am stuck up.
I found that PLC-2 Timer status dbit are little bit different.\\
Finally I mapped that Bit 17 in PLC2 equals Timer Enable in PLC5
Bit 15 in PLC2 equals Timer Done bit
Bit 16 is used as flasher.

But i want to know what bit 14 in PLC2 timer represent.
I searched manuals and could not find it.

My question is that Timer timing bit or something else.
\
I could only find bit 14 equal to Overflow and that too in counter and math instructions.

Hope some PLC2 gurus might help me about bit 14.

PLC is mini PLC2/16 .

thanks
 
PLC2, a long time back!

I could only find bit 14 equal to Overflow and that too in counter and math instructions
That is because bit 14 is only used in those instructions. The timer words have a bit 14 but it is not used for anything. If it were, the manual would have defined it for you.

The PLC2/16 manual says:
14 Overflow/underflow bit. It is set when the AC value of the CTU instruction exceeds 999 or when the AC value of the CTD
instruction falls below 000.

Hope this helps you solve your conversion problems.
 

Similar Topics

HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
Replies
12
Views
498
I have an old Sentry Palletizer (S/O Number 3007 / Serial Number 1172) that has lost its program as the backup battery died years ago. I can...
Replies
0
Views
173
HOW to communicate with OPTIX and Mitsubishi's Q Series PLC?? PLEASE HELP ME
Replies
0
Views
99
I have a network with 4 PLCs PLC1 is controllogix and PLCs 2-4 are compactlogix and they all need to communicate. The current way I have this...
Replies
8
Views
318
So to start off: I have no experience with PLC's, but I'm good at figuring stuff out, but I need some help to know if my PLC is just dead in the...
Replies
2
Views
160
Back
Top Bottom