Prover meters that I am familiar with are used in the petroleum custody transfer field. They are usually a large horizontal cylinder with a piston. The fluid is forced into the cylinder. The movement of the piston trips limit switches at either end. The volume in between the limit switches is a known volume. The temperature of the fluid is monitored. Based upon temperature and volume, a mass quantity is calculated. The same volume flows through the meter under test. The meter under test is usually a turbine meter or propeller meter with a pulse output. The meter is calibrated in pulses per gallon. This number is commonly called a k-factor. Based upon the results of the prover, the k-factor is recalculated to match the prover value. The test is run three times for repeatability.
As for PLCs, I have never seen them used but they could be. You would need a high speed counter input to read the output of the meter under test. Most meters are already connected to some kind of transmitter which provides excitation to the coil around the element and a display of pulses and GPM and standard GPM.
 

Similar Topics

Hello, I want to connect the Factorytalkview ME with rslogix500 to see the live response of HMI buttons in Rslogix500 ladder code . I am using PLC...
Replies
4
Views
43
I have a cell with a compact guardlogix as the plc and I have three hmi's and two vfd's on this cell. I been experiencing momentary comms faults...
Replies
10
Views
93
Hi, hope you doing well I am looking for SIEMENS PLCSIM equivalent in GE FANUC PLC, RX3i PLC thank you
Replies
2
Views
33
Hai, I'm working on Allen Bradely PLC RS Logix 5000 V20 i tried to communicate modbus communication with AB plc and RS 232 to Ethernet converter...
Replies
1
Views
55
Trying to learn PLCs going to start by buying an Arduino Opta Wifi to practice with but what's the PLC I should get next?
Replies
10
Views
255
Back
Top Bottom