PLC5 BTW/BTR for analog Input
bluenoser337
Apr 2003
Nova Scotia
391
I have an old PLC5 program with block transfers for many A/I cards. The "setup screens" won't come up because the modules were never added to the IOC. I believe it was set up long ago by entering the scaling and other values in the N7 registers. I can't find documentation on those BTW registers. I want to adjust scaling. BTR - R2/G6/M0 Control N7:10 Data N7:40 Len 20. BTW - R2/G6/M0 Control N7:15 Data N7:80 Len 37. Also, the BTR and BTW execute at the same time...which seems odd. Shouldn't the BTW be on 1st scan, or when I trigger it somehow? Thanks!!
Tell us the complete catalog number of the analog card you have. And it would also be helpful if you can post your .RSP file. And tell us which card you want to make changes to.
Or better yet add the card to your IO configuration and make the changes their.
Mickey...I'm not at the site and just discovered this lack of information. It is a 16 A/I. That's all I know right now. Does the N file info come with the card documentation? Thanks!
Operaghost and Mickey...thanks for that. I think this gives me exactly what I need. I think the A/Is probably are IFEs. Thanks again!! Also, I don't think the BTW and BTR in my first post both belong to the input card. Just realized that this rack is 2-slot addressing...I think there is an A/O alongside the A/I.
The BTR and BTW info you posted does sound like the 1771-IFE. Those are the right lengths for the IFE.
(waiting to hit submit reply to give Mickey a chance to type!)
OG
Dear Pros, Need help on converting PLC5 to Studio 5000.:bow: I found few BTW/BTR block pointing back to Rack 000, group 0, module 0, which should...
2,226
I want to use PLC5 to communicate with flex IO, using RIO. Before I proceed I want to clarify my confusion about the addressing scheme, as I am...
4,028
When performing a Block Transfer Write and Read operations from analog cards on a A\B PLC 5, is it recommended to utilize the error (ER) bit for...
2,850
This one has me climbing the walls right now... Should have been simple, toss a SDN scanner into the PLC rack, configure it up with RSNetworx...
2,906
I need to setup some bit transfers between two processors, similar to producing and consuming in control logix but I'm dealing with plc5. If it's...
1,866