we are using AB PLC 5/40 E .My question is
A)Is it possible to know PLC fault history directly from any status msg.( after the fault has been resetted)
B)If it is not, whether a fault routine can help to save the data so that the fault details transferred to some data files.. If it is so- how to confirm that the data file not being erased during power up(instead of reset if Mr.Bumba reset the power)
You are probably meaning if the CPU has a major fault.
The SLC500 has a "previous major error" status word for just this purpose, but unfortunately the PLC5 does not.
You can program a program file to store the major fault status word S:12 in another data file.
Set S:29 to the program file no to trigger that the program file is run once when a major fault occurs.
Another possibility is to have a HMI log the values of S:12.
No HMI in system.
i just want to confirm if the data words(s:12)are shifted in a new file..the value will remain after plc reset/power recycle..or not
Similar Topics
As the title states, whenever our PLC5 faults I'll reconnect to it, but I'm never given an option to download a fault log. I have a good battery...
Replies
3
Views
1,413
I am getting ''Bad system configuration'' fault from the Plc5 processor maybe three times a week or less or more. After getting clear this error...
Replies
7
Views
2,778
Hello, I have a remote IO rack communicating back to a plc5-40 processor via DH+ that has recently given me some strange issues. the rack has...
Replies
3
Views
1,840
Hello - I need to show PLC5 card status (comms, fault, etc.) in RSView32 and am not sure where to start. Any help would be greatly appreciated...
Replies
16
Views
6,727
I was wondering if anyone had experience with a PLC5/20 and the PID instruction faulting the processor while changing values in the setup screen...
Replies
3
Views
3,849
Back
Top Bottom