Power Flex 527 , safety inhibitor fault
SGPeruma
Apr 2024
Singapore
Power flex 527 Network based safety drive had faulty and alarm pop up SOS Code internal fault
Unable to set or clear the fault manually or through logic ,
Changed the module and configure IP and download with new drive ok .
How clear the fault or its hardware issue ?
I’m facing three different drive same issue
I haven't used networked safety on PowerFlex drives (yet) but here are a few questions:
1) Is it a new installation or existing that used to work
2) Since it's networked safety, is the safety PLC online?
3) If safety PLC is online, does it show that it's communicating with the drive?
4) If the safety PLC is communicating with the drive, is it sending its "safety ok" signal (whatever that looks like)?
5) Does the drive need its STO jumper installed while using CIP Safety over Ethernet/IP? (I'd have to find the manual for this drive to find out)
Hi Joseph
Thanks ,
It’s existing running application
Safety PLC able to online and connected to drive
The issue safety fault and drive automatically inhibits unable to reset .
There is any options to perform factory reset ?
I try to use drive executive application tool to connect the drive .. it’s able to identify the drive present but unable to connect
Those drives aren't officially supported with Drive Executive. You should download Connected Components Workbench (CCW) instead.
Do you have access to the safety PLC?
It's not SOS, it's S05 safe torque off fault.
is this using CIP safety or wired safety with the red terminals on the drive? If it's on the red jumpers, see what's wrong with the safety circuit and whether those terminals are getting 24v or not. If it's CIP safety, make sure the jumpers are removed (people frequently leave the jumpers in when replacing drives, it's a common mistake on CIP safety). then you'll need to verify the safety is good in the program from that point since it's all internal logic for safety.
Hi Joseph
Thanks ,
527 aren't programmed with ccw or drive executive, they are programmed directly in the studio 5000 program with controllogix/compactlogix
Hi all. Would anyone happen to have the Modbus register datasheet for the Honeywell/EnergyICT EIMFlex Modular Meter v1.11 We've 40 of these that...
72
I have an issue with Power Flex 525 during running processing, the VFD stopped suddenly while the PLC and VFD connection ok, VFD does not have any...
133
I am trying motor startup with pf525 drive by using wizard start over ethernet communication but during direction test it's showing control error...
195
i have a flashing yellow sts light. "Stop Asserted" message on one of my PF 753"s, but no bits set in parameter 961. The safety circuit tests...
210
hello everyone. I have a 525 VFD that works, the screen shows the output voltage and the output frequency but in UVW I do not have voltage...
190