powerflex 525 max frequency parameter via rslogix 5000

nmk34

Member
Join Date
Apr 2019
Location
texas
Posts
80
hello
i am trying to set the max frequency for the drive via rslogix 5000, but do not see that patameter in the rslogix 5000 drive paramerts?
the other question i have; can I change the max frequency in "Enable input button" limit in factorytalk view ME from the drive it self, by changing the max freqiency parameter in the drive directly?
 
Hi,

Do you have access to the AB Knowledgebase under a Tech Connect Contract?
There is a technote there (ID: QA54963 ) that explains how to do this.

You basically have to use a Message Instruction to set the drive parameter.
If it is only one parameter, then the message type is "Set Single Attribute".
It is possible to change multiple sequential parameters if needed.

The technote also refers you to this manual http://literature.rockwellautomation.com/idc/groups/literature/documents/um/520com-um001_-en-e.pdf
 

Similar Topics

Hello, Would anyone happen to know what parameter in a PowerFlex 525 to have the drive trip if the torque permissive set point is exceeded...
Replies
3
Views
482
Good Afternoon , I'm working on a project with a CompactLogix and PowerFlex 525's . I plan on having a HMI screen that will allow some...
Replies
8
Views
4,117
Fairly new to the drive so apologise for the layman terms. Textile machine uses PF525 VFDs to control motors. The speed of the drive is currently...
Replies
5
Views
124
Hello, I'm hoping someone can help me with understanding how to set/change these data types. We recently swapped from Invertek to AB drives...
Replies
1
Views
123
All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
Replies
2
Views
114
Back
Top Bottom