Powerflex 525 viewing Current on Panelview 7 plus

Kantzje

Member
Join Date
Apr 2015
Location
PA
Posts
4
When I added device Powerflex 525 to my project,The ( current tag) was not populated .How can I retrieve this data ?

Thanks Jeff
 
What tag are you referencing in your PanelView project, I believe you need to use N registers to get data from the PF525.

There is a TechNote on how to communicate and control the PF525, I will see if I can find it.

TechNote is QA52360, you will TechConnect to view it.
 
Last edited:
It sounds like you need to add OutputCurrent as an input in the drive definition. In the old days they called it Datalinks. Now I think it is just called Inputs and Outputs. The 525 definition in your project will need to have that declared. The drive itself will also need a parameter set to match that.
 
You can also use a MSG instruction to grab the Output Current as well.

Not sure on the exact MSG attributes, but a quick search should provide you that information.
 

Similar Topics

Fairly new to the drive so apologise for the layman terms. Textile machine uses PF525 VFDs to control motors. The speed of the drive is currently...
Replies
5
Views
90
Hello, I'm hoping someone can help me with understanding how to set/change these data types. We recently swapped from Invertek to AB drives...
Replies
1
Views
117
All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
Replies
2
Views
107
Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
Replies
5
Views
281
Im trying to teach a couple of labs on VFDs at a community college. We have some motor control trainers with P525s and 3 phase motors from...
Replies
2
Views
287
Back
Top Bottom