Good Morning ,

Had a PowerFlex 70 go bad . Uploaded the parameters to the HIM . Did not have the right drive replacement . The HIM says that the drive doesn’t match , can you somehow override that ?

Thanks so much ,
 
I have never tried a copycat with a different HP, but I have done it with different firmware levels. The message that came up was a warning, but it allowed me to continue. I am sorry, I don't remember the wording of the option to continue, but it did allow me to do it.
I just did this about three weeks ago. One warning: if you are changing the assignment of inputs from the factory setting, make sure they are off when you change their value. If not, a bit will get set in the drive and not get updated. Our application uses input 6 as an enable input. It happened to be ON when I set parameters. The factory setting for input 6 is Preset Speed 4. Because that input was on when I powered up the drive and changed the input 6 assignment, it kept the bit that selects Preset Speed 4 high and I could not change drive speeds even though I configured the speed reference source as Port 5. I had to reset the input 6 back to Preset Speed 4, then shut off the input, then reassign it back to Enable. That cleared the issue.
 

Similar Topics

Some guidance here would be appreciated. I'm commissioning a system that has several drives installed and configured. One of the motors/drives...
Replies
3
Views
8,848
Hello Everyone, I want to upgrade the firmware of Powerflex 40 from 5.001 to 6.002 can anyone tell me how can I do that?
Replies
0
Views
50
Hello, I am currently in the final week of my internship and I have encountered issues with communication between a PowerFlex 700 variable...
Replies
8
Views
237
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
Replies
3
Views
184
Hi, I'm currently having issued with a PowerFlex 252. It was working fine last week, and suddenly decided to stop working. When I go into...
Replies
2
Views
123
Back
Top Bottom