PowerFlex 70
RBergmann
Jun 2002
California
258
All ...
I’m currently trying to configure an AB PowerFlex 70 VFD. I've set what I believe are the correct paramters, but apparently not all I need. I only get a flashing green light.
I seem to be having difficulty setting up for two speed operation. I don’t have an external reference source like a 4-20mA or 0-10V potentiometer. I wish to use the two of the speed select inputs to select the operational Hz.
Here’s what I currently have set up:
  • Run signal on Input 2
  • 1st preset speed select on Input 4
  • 2nd preset speed select on Input 5
  • Jumper terminals 7 & 8
  • Use internal 24VDC supply
I have two relays (enabled from a PLC); one for the Run signal and the second for speed control, NC on 4, NO on 5.
I think the wiring is okay, I believe my issue is with the parameter settings.
Thank for any assistance.
Hi
Start source is if you want to start from a card like Ethernet device net etc or from the terminals.
The flashing green light means you have not started the drive.
I would look again at the wiring and have you the stop wired as you will need this even if it's a link.
Donnchadh
I re-examined the wiring and no, there was no connection to the Stop terminal #1. I also discovered that the wiring guy had mis-landed a wire that should have been on #2 to #3. Corrected the mistakes and now, all is okay. Thanks guys.
I've got a Powerflex 700 that doesn't like to get going in the mornings. This motor will run anywhere from 30 seconds to 5 minutes before it just...
169
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
271
Hi I was wondering I need to update the firmware of a 755 inverter does the drive hold the program on the drive and just updates the firmware or...
172
Hello everyone, I'm new here. First of all I just want to say that you guys are very knowledgeable and reading your posts on here has saved my...
176
Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
236