PowerFlex 70

RBergmann

Member
Join Date
Jun 2002
Location
California
Posts
258
All ...

I’m currently trying to configure an AB PowerFlex 70 VFD. I've set what I believe are the correct paramters, but apparently not all I need. I only get a flashing green light.


I seem to be having difficulty setting up for two speed operation. I don’t have an external reference source like a 4-20mA or 0-10V potentiometer. I wish to use the two of the speed select inputs to select the operational Hz.

Here’s what I currently have set up:


  • Run signal on Input 2
  • 1st preset speed select on Input 4
  • 2nd preset speed select on Input 5
  • Jumper terminals 7 & 8
  • Use internal 24VDC supply

I have two relays (enabled from a PLC); one for the Run signal and the second for speed control, NC on 4, NO on 5.

I think the wiring is okay, I believe my issue is with the parameter settings.

Thank for any assistance.
 
Hi

Start source is if you want to start from a card like Ethernet device net etc or from the terminals.
The flashing green light means you have not started the drive.
I would look again at the wiring and have you the stop wired as you will need this even if it's a link.

Donnchadh
 
I re-examined the wiring and no, there was no connection to the Stop terminal #1. I also discovered that the wiring guy had mis-landed a wire that should have been on #2 to #3. Corrected the mistakes and now, all is okay. Thanks guys.
 

Similar Topics

Fairly new to the drive so apologise for the layman terms. Textile machine uses PF525 VFDs to control motors. The speed of the drive is currently...
Replies
5
Views
122
Hello Everyone, I want to upgrade the firmware of Powerflex 40 from 5.001 to 6.002 can anyone tell me how can I do that?
Replies
0
Views
65
Hello, I am currently in the final week of my internship and I have encountered issues with communication between a PowerFlex 700 variable...
Replies
8
Views
241
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
Replies
3
Views
186
Hi, I'm currently having issued with a PowerFlex 252. It was working fine last week, and suddenly decided to stop working. When I go into...
Replies
2
Views
135
Back
Top Bottom