Robot Teach... Safety Requirements?
Nov 2007
North Yorkshire
26
I have a project with a large array of servo drives, as part of the setting up sequence i want to follow the way robot's work during teach mode - ideally during setup reducing all the drives into a "reduced power/speed" mode and allow access into the hazard zone without tripping the lazer scanner protecting the area.
My main thought however is how do you safely set a drive to "reduced power/speed" etc, i can set a definative input on the CNC controller to overide any commands from the program but can it be classed as safe if you are relying on the CNC controller?
How do robot manufactures get around verifiying its safety??
I would be keen to know if any one has had any similar issues in the past or has any suggestions??
I'm not sure how this applies but the robots I am around have a deadman switch on the pendant. The pendant must be in hand and the switch is moved to the halfway point of its action in order for the servos to come in. Any operation other than that requires all safeties to be functioning properly like safety gates closed, light curtains clear, pressure mats clear, etc.
Thanks for the replys...
I did consider going down the "deadman's handle" but after speaking to the operators/customer some of the operations such as tooling changes require two hands free.
We are planning on using Baldor moti-flex drives with a nextmove e100 controller all linked together with ethernet.
Any other suggestions welcome?
hokie said:
You need a servo drive with category 3 safety, that supports safe motion.
They have a redunant saftey board that monitors the motion along with drive. A few manufacturers make that type of product. See below link:
http://www.boschrexroth.com/busines...indradrive_en/sicherheitstechnik_en/index.jsp
This explains it perfectly. The Fanuc robots I'm programming now will not allow the servos to run over 250mm/sec when the teach pendant is enabled and the deadman switch on the back of the pendant comes into play with the E-stop circuit. There is also a optional deadman switch to allow a 2nd person in the cell.
I guess the only other way is to design the mechanical part of the system in such a way that nothing moves on its own when the servos are disabled. Which could mean, depending on situation, motors with brakes, disengaging air springs etc.
I am yet to see a servo manufacturer that would offer a drive with "safe lock" function - some kind of safety-rated circuit that would keep servo enabled at zero speed rather that disable it. Then, a combination of a keyswitch, gurads bypass relay and a deadman switch might be used for slow jogging.
I would have to agree with ladderlogic,
i have not seen one system that would have control reliable speed limit function in the drive. one can use safety circuit to send signal to drive to enable speed limiting (via external speed reference or drive parameter) but this is still not safety rated input/function.
teaching is manual function (so be alert and hold on that enabling device aka dead man switch). standard these days is 3-pos switch which enables drives if the switch is in mid position (squeezing or releasing causes safe stop).
if anyone is aware of motion system that works differently (has control reliable speed limit functuion), i would like to know about it.
I have done this before...
You can buy drives that allow EN954-1 category 3 safe motion from many manuafactures: Bosch Rexroth, B&R, Siemens, Lenze ...
They cover things like safe limit velocity, safe motion limits, incremental distances, etc. This is been availible for several years.
This is seen on many CNC machines for setup, printing machines for threading, Robot cells for teaching points with operators in the work cell, etc.
do you have sample part number? i'd like to check that out.
there is number of drives out there that have "safety integrated" etc meeting Cat3 but this was always only for drive enable, nothing else...
thank you. i've read the link and checked documentation (have bunch of big manuals) but
still can't find how to limit speed - on demand - and safely...
any pointers?
Here is a manual on how to do it with G120 their regular VFD drive. I belive its the same principle with the Servo's. You set up safe parameters with the configuration software for the servo and then you send commands over profisafe (Profibus or Profinet) to go down to safe speed and then the drive does all the monitoring and shuts down in case of fault. I'm actually going to use a S120 with safe speed in an aplication so in a couple of weeks i will know exactly if you need any examples.
Good Evening , We have a Fanuc LR Mate . Our operators have the habit of grabbing hold of the robot to clear a crash , or find the witness...
4,099
Hi, folks, how are you? Is there some way to lock/freeze Fanuc robot teach pendent? Since some of our operators jumped program lines with teach...
1,735
Hi, i have a fanuc robot with a R-30ia mate Open air controller, and a broken teach pendent (TP). is it possible to disconnect the TP and make a...
2,585
Quick question to those of you who deal with robots on a daily basis. How do you handle the teach pendant cables? They always end up in a...
4,200
hello, I'm a student and for my final grade I have to repare a sepro robot. the only problem I have for now is that i have an error code 3...
57