Rockwell MAPC instruction
aand74
Dec 2005
Deinze
131
In a Siemens controller when I have a cam where f.i. master- and slave position is absolute, when the the camming is started the slave will first in a sychronisation phase go to it's start position in the cam. From there on master and slave position will be exactly (absolute) as in the configured cam.
I have done now some tests with Rockwell and the MAPC control.
So far I see no way to setup the instruction that when starting the cam the master and slave will always be in an absolute position as in the configured cam.
If f.i. my cam starts with a slavevalue of 10.0, but the actual slave position is 7.0 when starting the cam, there will be no synchronisation phase that eliminate the position difference of 3 mm (as in Siemens).
Is the only way to achieve that the slave position is absolutely the same as in the cam, to position the slave to the start position of the cam before starting the cam?
Good Morning , I'm having a problem with a Kinetix Servo MAPC instruction. I keep getting a #85 Fault. Could you give me some...
1,691
1,128
If f.i. the slave axis has to start the camming not from the beginning of the cam but somewhere in between, the parameter 'cam lock position' has...
1,431
I have a PH meter that I am trying to bring its data into 1756-L81. I have downloaded the Rockwell MODBUS AOI kit, but I am not sure if I need to...
168
Hi all. Customer wants analog faceplates really bad, even if we explained that it doesn't make much sense in his process. What he wants to see...
129