I have a s7-200 that I am using to gather some production data from a process. But if I make changes to the program I lose any gathered data (Real numbers and single letter strings that are set via a TD200C). Although all retentive counters in the program do retain their value.
The ranges are set to be retentive in the system block but I think this only applies to retentivity after a power loss.
So my question is, can I keep this data intact when I download a new modified project to the PLC...?
So simple when you know how....... Thankyou.
Is it just me, or is the Siemens website impossible to search and get what your looking for....? Lots on there, but a pain to navigate.
Thanks again for the info.
Its not you, it takes some getting used to and even then sometimes you still cant find what you are looking for!
The other way to achieve what you want (and the way i prefer) is to create a DATA BLOCK from ram. It requires you stop the processor to upload, but at least you have the latest parameters stored.
I get into the habit of regularely doing this when commissioning, and find it's better to have a more up to date version of the offline & online files...
Hope this helps.
Rob
Thanks for the info...
Kidblue
Does this then mean that after I "Create data block from RAM" the data block on the PC will now display values stored within the PLC? I ask because this would be a quick way of capturing the current stored data that otherwise would have to be displayed in Status chart?
Dear Experts, Please, kindly guide me through how to read data from ABB PLC to S7-1200 Siemens PLC. I want to use Siemens S7-1200 PLC to read data...
461
Hi, I have a s7-1200 at home that went into "CPU error: Serious firmware exception". After a power cycle it was OK again, but all retained data...
854
Hi to all, I have a power supply "gwinstek" PSP-2010, with rs-232, so I want to control it with S7-1200 "1212acdcrly with CM-1241 RS-232 module...
1,463
Hello all, I am working on a project utilizing an s7-1200 cpu and Tia Portal v17. I currently have an external PCB with some sensors on it (and...
745
Need some insight into why this happened. After finally getting a VM to connect to a CPU 216 2 siemens processor, uploaded the program. made a...
2,584