s7-300 analog reading
tulip
Oct 2005
ist
236
I'm using FC105 Scaling block for analog periphery reading.Are there any reading difference of betweens voltage,current,resistor,thermocouple for scaling?
That is ;is it enough directly PIW using?.. Thanks in advance...
Siemens works with an input integer from 0 to 27648. This can correspond with 0 to 10V, 4 to 20mA, 0 to 20mA, depending on what your settings are in the hardware config.
More can be readed on the page KalleOlle has given.
The FC105 only does a simple math calculation.
It devides PIW by 27648 and then multiplies by your range and adds an offset.
Formula from Siemens manual:
OUT = [ ((FLOAT (IN) – K1)/(K2–K1)) * (HI_LIM–LO_LIM)] + LO_LIM
You can use FC105 for voltage and current inputs as mentioned above, but the thermocouple inputs are usually scaled directly in 1/10°C.
In other words an input value of 279 is equivalent to 27.9°C.
I have a client who has asked for a pop-up for each of their analogs, which will display the alarm values. The values displayed in the pop-up...
2,541
hi i am using s7-300(CPU 313c). when i try to use FC106 unscale function, i can change IN manually but there is no effect on OUT. i wrote PQW752...
1,612
Hi guys, I have CPU S7-300-313C ( Cat No - 6ES7-313-5BE00-0AB0) DI24/DO16 and AI5/AO2. when I am trying to configure and use the AO channel PQW...
2,567
I am a student. I can program PLC using LAD language using digital IO. But, I want to program using analog IO also. We have analog IO module with...
2,080
Hi All I am using 2 x analog cards on my rack and they are described as 12bit cards in there title. The manual suggests that the resolution can...
2,038