Scheduling a DeviceNet on CompactLogix bus
ettikudiappan
Apr 2002
Singapore
131
Hi
I have 2 machines from the same vendor, but one was received a few years before the other. The newest machine, allows me to schedule a DeviceNet network using DH485 PIC driver and the older one doesnt allow me to do so.
The Older Machine setup is as follows
1) Controller is 1769-L30/A 5330, Revision 11.27
CH1 configured as DH485
2) DeviceNet module is 1769-SDN
3) CH1 of controller connected to AIC+, 1761-NET-AIC Ser B
4) PC with PIC driver configured is connected to AIC+ module
The Newer Machine setup is exactly same as older machine except we are using 1769-L31 5331 controller, Rev 13.15
Using the new machine, I can browse to the backplane and expand the SDN card to reach the Devicenet network to schedule it using RsNetworx.
Using the older machine, I can only browse upto the Devicenet scanner module but not to the network.
Is there a simple way (Firmware upgrade etc) to enable me to use the existing hardware to schedule the older machine. Else I need to buy 1784-PCID card for my PC and 1787-PCABL cable to connect to the Devicenet network.
Hope someone can help.
etti
You are correct. The first-generation CompactLogix controllers (the 1769-L20 and -L30) did not support networking passthrough to the 1769-SDN.
All the second-generation CompactLogix, including the 1769-L31, L32E,- L32C, -L35E, and -L35C, as well as do the third-generation -L43 and -L45 controllers support full network bridging.
You need a 1770-KFD module or 1784-PCD module to directly access the DeviceNet, or browse through another Logix network interface to access the network.
Dear Experts, Thanks in advance for your kind help. I have a GEO SCADA expert 2022 and configure it as a DNP3 master, also I have multiple DNP3...
606
Hi all, New grad working with PLCs for the first time. Today I came across the concept of scheduling when adding new devices to a ControlNet...
1,085
Hi, I am looking at the setting up some new ethernet comms which is originating from an SLC 5/05 to four new identical CompactLogix L24ER's...
2,540
I have a question in regard to taking a ControlLogix L62 PLC (v.16) offline that is currently using controlNet for communications to VFDs etc...
2,541
Dear All, We have redundant system with 1756-L61 with Control net module CNBR/E, Our both Controllers are in healthy state and RM modules are in...
1,384