I've been tasked by my supervisor to make a connection and do some testing with Vijeo-Designer (Web Gate specifically) and a Magelis Touchscreen.
I've been able to use Internet Explorer to connect to the Magelis and look at my Variable Table and HMI screens remotely. However, I am not seeing any of the integers listed in my Numeric Displays, and specific shapes that rely on variables to change colors (showing if an integer is within a specific range, for example) appear to be grayed out. Also, a large graphic that relies on the state of a Bool Variable is displayed regardless of the Bool's state.
Here's some pertinent information;
-I am using Vijeo-Designer V6.2.1.189.
-I am using Magelis GTU series HMIG3U Touchscreen
-I have set all variables used in the project to Read/Write until this is solved, then I will revert the variables that aren't changed with the program back to Read Only
-I have checked many times that the integers and Numeric Displays are set for Enable Input
-The HMI displays normally, regardless of what the Web Gate displays
-While trying to change some integer values from the Web Gate, an error message is displayed stating "Attempted IO operation (write) on a READONLY variable. xxxname_of_variablexxx
-I have gone through the HMI settings, entered Remote Access, enabled the Web Gate to accept any IP address attempting a connection, and tried to change all Publish Property settings to "ALL". After clicking "OK", those settings revert back to "NO CHANGE". I was concerned at first, but the "PublishTo" setting for all my panels are set to "ALL".
-I have gone into my firewall and checked that ports 80 and 6000 are being forwarded, and they are.
Looking at the help files for Vijeo-Designer has been exhaustive, and I am no closer to figuring this out. If anyone has some suggestions on what to try next, I welcome them. Thank you.
I've been able to use Internet Explorer to connect to the Magelis and look at my Variable Table and HMI screens remotely. However, I am not seeing any of the integers listed in my Numeric Displays, and specific shapes that rely on variables to change colors (showing if an integer is within a specific range, for example) appear to be grayed out. Also, a large graphic that relies on the state of a Bool Variable is displayed regardless of the Bool's state.
Here's some pertinent information;
-I am using Vijeo-Designer V6.2.1.189.
-I am using Magelis GTU series HMIG3U Touchscreen
-I have set all variables used in the project to Read/Write until this is solved, then I will revert the variables that aren't changed with the program back to Read Only
-I have checked many times that the integers and Numeric Displays are set for Enable Input
-The HMI displays normally, regardless of what the Web Gate displays
-While trying to change some integer values from the Web Gate, an error message is displayed stating "Attempted IO operation (write) on a READONLY variable. xxxname_of_variablexxx
-I have gone through the HMI settings, entered Remote Access, enabled the Web Gate to accept any IP address attempting a connection, and tried to change all Publish Property settings to "ALL". After clicking "OK", those settings revert back to "NO CHANGE". I was concerned at first, but the "PublishTo" setting for all my panels are set to "ALL".
-I have gone into my firewall and checked that ports 80 and 6000 are being forwarded, and they are.
Looking at the help files for Vijeo-Designer has been exhaustive, and I am no closer to figuring this out. If anyone has some suggestions on what to try next, I welcome them. Thank you.