Series 90-30 GE ,Error 8036
sultanahmed
Jul 2013
home
63
Hi Every one,
while PLC program uploading Ge fanuc CPU 90-30 CPU 313 having built in cpu 5 slots rack mounted and module ic693apu301 is attached with it , getting this error code.
dont know what exactly error is.
IC693APU301 picture is attached
Indication of module:
EN1 ON
EN2 OFF
stat ON
ok ON
cfg ON
Uploading from the connected device
Error 8036: Address '%AQ0002' on 'AQ0002[0]' is already used on 'AQ0001[1]'
Error 8036: Address '%AQ0003' on 'AQ0002[1]' is already used on 'AQ0001[2]'
Warning 8022: Type mismatch between variable and instruction. [LD Block,'ALLARMI': Rung 19]
Uploading: CONFIG VERSION
Uploading: REF MEMORY ALLOC
Uploading: RACK SLOT CONFIG
Uploading: I/O CONFIG
Uploading: SNP ID
Uploading: _MAIN.dec
Uploading: _MAIN.pdt
Uploading: COMBIT.pdt
Uploading: COMWORD.pdt
Uploading: PROFACE.pdt
Uploading: ALLARMI.pdt
Uploading: SINCRO.pdt
Uploading: Values - %R
Uploading: Values - %AI
Uploading: Values - %AQ
Uploading: Values - %G
Uploading: Values - %M
Uploading: Values - %Q
Uploading: Values - %I
_MAIN.pdt Processed successfully.
COMBIT.pdt Processed successfully.
COMWORD.pdt Processed successfully.
PROFACE.pdt Processed successfully.
ALLARMI.pdt Processed successfully.
SINCRO.pdt Processed successfully.
Building block: _MAIN....
Size of Logic Binary File = 165 Bytes
Successfully processed.
Building block: COMBIT....
Size of Logic Binary File = 168 Bytes
Building block: COMWORD....
Size of Logic Binary File = 249 Bytes
Building block: PROFACE....
Size of Logic Binary File = 202 Bytes
Building block: ALLARMI....
Size of Logic Binary File = 297 Bytes
Building block: SINCRO....
Size of Logic Binary File = 362 Bytes
---------- Post Processing ----------
%R Initial Values
%AI Initial Values
%AQ Initial Values
%G Initial Values
%M Initial Values
%Q Initial Values
%I Initial Values
---------- Upload from Controller completed ----------
Preparing target for import
Importing Hardware Configuration...
Importing Folder File...
Importing Smart Store...
Importing Variable File...
Importing block ALLARMI...
Importing block COMBIT...
Importing block COMWORD...
Importing block PROFACE...
Importing block SINCRO...
Importing block _MAIN...
The selected memory was successfully uploaded from the connected device.
Please Expert your opinion and expertise required thanks in advance.
It looks like %AQ1 & 3 are configured as DINT most likely in the APU but %AQ2 & 3 are also referenced and/or used in logic. If the program has been running properly ignore this and set Prophecy ME to ignore it also.
The photo looks like you need a new RAM backup battery, so don't turn off power to this unit until it is changed or you could lose the program and register data.
Ic693apu301
Hi Russ,
Thanks for your expert opinion. i set controller duplicate address as ignore,when i go online and try to upload program target is not equal,i check rack cpu and module numbers position still program is not equal,
Picture and program is attached.
I am using machine edition 8.5 version.
1) i am bit confused why my program is not equal with actual????
2)do i require for APM Vmware???
what i get in from feed back zone is:
Uploading: SNP ID
%R Initial Values
%AI Initial Values
Variable _%AI0005 has been created
Variable _%AI0013 has been created
Variable _%AI0014 has been created
%AQ Initial Values
%G Initial Values
%M Initial Values
%Q Initial Values
%I Initial Values
Please Experts help required.
Thanks in advance..
  • mri machine on.zip
There may be a stored motion program in the APU301 module and that might be the reason for the configuration inequality.
Select the module in the navigator, press F1 for module-specific help and then go to the selection "Integration of the APM Motion Programmer to Machine Edition" for details about how to retrieve the stored program.
Hi, I have a project with a R04CPU, RD77GF16 and a RJ71PN92 modules. The cell is given to me to change the program since the previous integrator...
305
One of the Q68DAIN modules (analogue output) has an ERROR light on...rack 0 slot 11, see picture. I cycled the PLC power which cleared it for a...
1,902
Hi everyone, I'm currently configuring a Q-series PLC (Q10UDEHCPU), using GX Wroks 2, and a Q71E71-100 Ethernet communication module to...
2,252
Hi, Quick one passing through as I'm quite busy at the moment... Two-day head scratcher here trying to flash upgrade a bunch of out-of-the-box...
10,979
I keep getting a Net IO error message F037 on a brand new drive and after researching it, AB says that it has to be connected to a managed...
2,301