The Physical Details:
Network 1: Rockwell
- EN2T 192.168.1.102
- Red Lion Built in Ethernet port 192.168.1.125
- Rockwell VM - 192.168.1.247
-- all subnet 255.255.255.0
-- Gateways 0.0.0.0
--- Everything pings fine and get data in local tags in Crimson

Network 2: Siemens
- Onboard port X1PR1 - 192.168.0.1
- Redlion Expansion port 192.168.0.20
- Siemens VM 192.168.0.223
-- all subnet 255.255.255.0
-- Gateways 0.0.0.0
--- Everything pings fine Get N/A in Value when looking at online value in Crimson.

I set up a program in the G3 HMI to ping the Siemens PLC from the Redlion. This returns successful.

The only documentation on Red Lion's website says you need to disable protection (set to full access), enable PUT/GET and disable Optimized block addressing. I have done those 3 things. Red Lion tech support was stumped.

Any Ideas?
 
Siemens S7 TCP/IP Master with TIA S7 Tag Import.

Red Lion tech support confirmed that is the only TCP/IP one that will work with the 15xx processors.

We've thought of adding the profibus card to the red lion but that is the nuclear option at this point...
 
Siemens S7 TCP/IP Master with TIA S7 Tag Import.

Red Lion tech support confirmed that is the only TCP/IP one that will work with the 15xx processors.

We've thought of adding the profibus card to the red lion but that is the nuclear option at this point...

How are the tags imported? is it an online import or an offline import?

Are you addressing the tags by their tag name, or by their DB number and address?
 

Similar Topics

Hi! What is the way to convert the code from the Codesys code to the Tia Portal? Regards, WK
Replies
4
Views
73
Good Afternoon , It has been decades since I have done anything with Siemens . What is the Siemens name of their Servo Product Line and what...
Replies
10
Views
208
I'm using the Siemens PRONETA software to do some IO testing currently. I love the simplicity and fast testing capability. Does anyone know about...
Replies
0
Views
87
Hi, First time user of S5 Siemens. Is there any solution on how to solve this kind of error. HMI OP7 $613 DB-error No. 11 (0: 15) Siemens PLC...
Replies
9
Views
173
Hello, I have an issue where I want to simulate an Siemens HMI panel, through NAT connection to a PLC. I have the possibility through extended...
Replies
8
Views
260
Back
Top Bottom