Siemens 1517F-3 and Redlion DSPZR Communication issue
telos
Aug 2017
USA
The Physical Details:
Network 1: Rockwell
- EN2T 192.168.1.102
- Red Lion Built in Ethernet port 192.168.1.125
- Rockwell VM - 192.168.1.247
-- all subnet 255.255.255.0
-- Gateways 0.0.0.0
--- Everything pings fine and get data in local tags in Crimson
Network 2: Siemens
- Onboard port X1PR1 - 192.168.0.1
- Redlion Expansion port 192.168.0.20
- Siemens VM 192.168.0.223
-- Gateways 0.0.0.0
--- Everything pings fine Get N/A in Value when looking at online value in Crimson.
I set up a program in the G3 HMI to ping the Siemens PLC from the Redlion. This returns successful.
The only documentation on Red Lion's website says you need to disable protection (set to full access), enable PUT/GET and disable Optimized block addressing. I have done those 3 things. Red Lion tech support was stumped.
Any Ideas?
Siemens S7 TCP/IP Master with TIA S7 Tag Import.
Red Lion tech support confirmed that is the only TCP/IP one that will work with the 15xx processors.
We've thought of adding the profibus card to the red lion but that is the nuclear option at this point...
How are the tags imported? is it an online import or an offline import?
Are you addressing the tags by their tag name, or by their DB number and address?
Good morning, all I am very new to siemens family and to STL, i have been playing for two days now and manage to get the scaling do in STL. Now...
73
Hi! What is the way to convert the code from the Codesys code to the Tia Portal? Regards, WK
123
Good Afternoon , It has been decades since I have done anything with Siemens . What is the Siemens name of their Servo Product Line and what...
217
I'm using the Siemens PRONETA software to do some IO testing currently. I love the simplicity and fast testing capability. Does anyone know about...
93
Hi, First time user of S5 Siemens. Is there any solution on how to solve this kind of error. HMI OP7 $613 DB-error No. 11 (0: 15) Siemens PLC...
178