Siemens Drive G120 IO address
Holmux
Oct 2013
Aalborg
279
Hi All
CPU 1517F-3, Drives G120C
Working on a project that is under development, so more IO will be added as we go along, to keep my drives out of the way, I would like to address the IO for the drives from a 1000 and up, I have around 120 drives.
Is there a trick I can use, I have tried to set the IO for the first drive and copy/paste to see if it would add from there, but it jumps back to the first available address.
Is the long way, the only one, where I go into each drive to set the address?
/Holmux
120 drives !
I have never had that many.
I dont know a trick to automatically have a certain range.
The easiest way to edit the IO addresses is to open the Device View of the CPU that controls the drives, and then pull out the pane in the righthand side called Device Data.
The IO addresses can then be edited in a list instead of having to open up the properties of each device.
I'm sure I've seen a tick box somewhere to set things to follow the next available IO numbering, but not only can I not remember where it is, because it's a tick box I don't think it's configurable to that level.
You could try adding a pile of fictional analog units to take up all your IO numbering and then remove it all once the drives are in.
Yes, it will allocate the next free address following the copied drive. (tested using TIA V17)
I think what OP is saying is that they have plenty of free space in their project, but all drives need to be address 1000+
Drive 1: 1000-1020
Drive 2: 1020-1040
etc.
But what it's doing is allocated Drive 2 to say address 14-34 instead because that's also free.
I've just done it in TIA Portal V15.1 and when I copy and pasted a drive it took the next addresses to the one I had copied from.
So What LD said is correct.
Cheers
Mark
Thanks for the feedback.
I think maybe V15.1 works differently, or it is a setting somewhere.
I have the same issue as Holmux, but it is not so aggrevating to me since I dont have 120 drives :)
I haven't changed any settings.
I had a drive that started at IW980 and ended at IW998.
Copied this drive and pasted, and the addresses started at IW1000 and ended at IW1018.
Same with the ouptuts.
Albeit this is with a Danfoss drive, but I suspect its the same.
Cheers
Mark
Cheers
Mark
I have tryid all combinations, adding a few drives in the right order above 1000, but *** soon I make a copy/paste I am back to first available address.
All the other equipment I have on the profinet, I have been able to copy/paste the unit and the address follow up I order, but not with these drives :☹
Hi All I have done the commissioning wizzard on the drive with Tia portal V15.1 and all good , but once i go to acceptance test and click on STO...
2,226
Kindly, has anyone tried to control Lenze servomotors with Siemens S120 drives ? Any special hints ? Have some concerns for the resolver and servo...
249
On my machine we have MicroMaster 6SE6400-1PB00-0AA0 running a motor with a Siemens 6FX2001-5QP24 encoder. Everything was working fine and then...
302
I have G120 with Firmware version V4.7.13. In the TIA project, I have version V4.7.10. I would like to install new firmware HSP in my project. I...
1,929
I have a new Siemens DCM Drive and I need to know how to make it run Forward Only. I can do this if I turn the torque to 0 but I need the negative...
4,277