Siemens S7-312C retentive memory

Pego

Member
Join Date
Feb 2005
Posts
117
A client asked me to modify an existing system.
It is a Siemens S7-312C compact CPU and a OP3 text display.
Now the bitmemory MB0 to MB 60 is used to store variables that can be changed via the display.
But this range is far too small for the variables I want to store, so I want to use DB1 for this.
In the hardware configuration->properties->Retentive Memory I can not select any DB however....
Are the DB's automaticaly saved when the CPU powers-down?
I can not imagine that the 128 bytes of bitmemory is all that can be used to store data.....
Just want to be shure before I tell my client things I can not realize.
I hope somebody can tell if I can use DB1 for this or not.
PG
 
I don't have the manuals at home and I'm not going to be in the office for the next few days, while I don't know the 312, I'm pretty sure that in all the modern MMC based 300 CPUs the DBs are retentive.

You should get confirmation from our resident S7 gurus before lunch!
 
I believe all DB's will be retentive unless specified (I might be wrong on that), or maybe just up to DB511

Right click a DB block and select properties, then select the 'general part 2' tab and check to see if the 'non-retain' box is unchecked.

The picture below might help

Paul

db_retained.jpg
 

Similar Topics

Hi! I have a question regarding ethernet communication with a Siemens S7-312C and 343-1 Lean. For some time I´ve been using the S7NetPlus...
Replies
8
Views
3,327
Hello I have a Siemens s7 312C PLC and a IBM PC with Simatic S7 V. 5,4 Sp 3 installed. I have got a USB / MPI cable from China. But it does´nt...
Replies
4
Views
4,647
I have never had the pleasure of working with a "Thermistor" until now and have a question. The Thermistor is a 10KOhm 4-20mA 2-wire device and I...
Replies
3
Views
74
Hello, I have a CPU 317-2DP Firmware Version V2.1.8. In TIA Portal only V2.6 is available, and there is no option to upgrade FW. Then I open it...
Replies
9
Views
176
HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
Replies
12
Views
432
Back
Top Bottom