Hi
I have used a lot of these in a multi instance function block for alarm debouncing. However if the customer does not wish to use a debounce, my intention was they just set 0 as a preset. However I have found that if a value of 0 is used the timer output does not turn on. All the presets come from a MP370 WinCC Flex.
What is a preferred way of turning on the 'timer done' bit in this situation?
I am considering checking if 0 is entered and overwriting it with 0.1 in the PLC or modifying the HMI to use scripts to do the same thing
Cheers
I have used a lot of these in a multi instance function block for alarm debouncing. However if the customer does not wish to use a debounce, my intention was they just set 0 as a preset. However I have found that if a value of 0 is used the timer output does not turn on. All the presets come from a MP370 WinCC Flex.