Siemens works only after opening licence manager.
rigicon
Aug 2009
kent
415
Hello forum,
Question about Automation manager for Siemens. I upgraded to Automation manager 4.0 SP2. I use to just click the simatic icon and it would load up. Now it gives me an error saying can't find a valid licence. If I open up Automation licence manager minimize then run siemens it works. Is this a new thing or is the install faulty?
here's a screen shot of Automation manager.
Annoying but still works. Must be a solution....o_O
Oops someone else has had the same problem LINK
So it seems I must roll back to Automation manager 3.
Or has siemens sorted the problem?
I also ran into the same issue. The problem is when you use 4.0 you must enable the manger service. This is done thru your control panel. Once you have the Siemenas Licence manager starting and running as a service 4.0 works fine.
Clay B, I checked it is running as a service and it is started. From power on - I run automation manager then close it everything works. From power on - service is running not working until I run automation manager once then it all works.
When you say through your control panel do you mean computer , manage then services or should i make the program start up from power up.
New to S7. Are the "Network 1/2/3/..." simply individual "rungs" of the ladder or is there more to it than that? Thanks
554
I know what it is doing, it is creating P#DB104.DBX48.0 Byte 32. This is later used in an SFC14 block further on. I just can't wrap my head...
1,628
In TI8 portal...I notice there are "Networks" and rungs used. You can have more than 1 rung in a Network and you can have multiple Networks...
2,933
I have two PLC's networked together over an PN/IE_1 network. They both have separate IP addresses and are declared as such in the Device &...
7,486
I've never looked at a Siemens TI505 series plc program until now. On a rung is a function call block for a SFPGM. I found in the Programming...
3,055