CPU: 5069-L330ER v32
HMI: PV+7 10" v11
Every time the customer powers off the machine and re-applies power, the HMI gets stuck on Starting Application.
If you open FT Studio or try to save the Studio 5000 whilst on-line, you get all the errors messages and symptoms as per this tech note:
https://rockwellautomation.custhelp.com/app/answers/answer_view/a_id/1089948/loc/en_US#__highlight
For those without Tech Connect, the FT Studio Errors are:
"Failed tag information upload on route cip=<path> at <IP address> and Symbol upload ends with error for CIP=<path> at <IP address"
PLC Save Error:
Error 732-80044402 - Data upload did not complete. CIP Error: Address offset out of range.
As per the tech note, I rebuild the project and download again, all the errors disappear and the screen springs to life again.
It offers a solution but no root cause of how to fix the issue.
Anyone else experienced this error before?
HMI: PV+7 10" v11
Every time the customer powers off the machine and re-applies power, the HMI gets stuck on Starting Application.
If you open FT Studio or try to save the Studio 5000 whilst on-line, you get all the errors messages and symptoms as per this tech note:
https://rockwellautomation.custhelp.com/app/answers/answer_view/a_id/1089948/loc/en_US#__highlight
For those without Tech Connect, the FT Studio Errors are:
"Failed tag information upload on route cip=<path> at <IP address> and Symbol upload ends with error for CIP=<path> at <IP address"
PLC Save Error:
Error 732-80044402 - Data upload did not complete. CIP Error: Address offset out of range.
As per the tech note, I rebuild the project and download again, all the errors disappear and the screen springs to life again.
It offers a solution but no root cause of how to fix the issue.
Anyone else experienced this error before?