Hey!
Quick question. Is there a quick and easy way of recurrently move safety inputs to a DINT for example?
This is the idea but for obvious reasons it doesn't work...
for Position 1 to 10 do
for Index := 0 to 7 do
Data[Position].Index := SafetyInputs: (Position):I.Pt0(Index)Data;
end_for;
end_for;
Thanks!
How about :
For zzpos := 0 to 10 do
zzdata[zzpos].0 := Local:1:i.Pt00.Data;
zzdata[zzpos].1 := Local:1:i.Pt01.Data;
zzdata[zzpos].2 := Local:1:i.Pt02.Data;
zzdata[zzpos].3 := Local:1:i.Pt03.Data;
zzdata[zzpos].7 := Local:1:I.Pt07.Data;
end_for;
EDIT:
Nevermind.. its doesn't change the Local:"X" number...
Also... why do you need to do this? simplify an HMI screen?
Hey!
What triggered my curiosity was indeed an HMI application. It's a bit time consuming the way it's done now and, if I may say, not elegant. I was curious if I could go in a different direction to simplify (shorten) the code...
Thanks!
When I have to do that I create a global object and use parameter definitions.
I've done it a lot for customer who still demand IO status screens the old fashion way.
For example, I can put the module, slot, and point all as different parameters.
I'm assuming you using a AB Panelview with FactoryTalk View Studio...
I would create a global object indicator, and use different parameter definitions.
So something like #1:#2:#3:pt#4.Data
And for the parameter definitions #1 would be Module (Local for Example)
#2 would be slot number, #3 I or O, #4 bit address.
So for Local:2:I:pt05.Data, the parameters would be
#1 = Local
#2 = 2
#3 = I
#4 = 05
The good thing about View Studio it lets you manipulate the tag names like that.
Then put the global object on a display, put in the parameters you want (I usually put a weird character in the slot like '$'), work on the first group of 8, then make multiples of those groups, and once you have enough for all the IO, just select a group of 8 and put replace the $ with the slot number.
Hey!
The way you described is pretty much how the HMI application is working now for PV the difference is that the inputs are already in DINT bits which are also manipulated on PLC logic...
Thank you again!
Hi, I have this weird issue whenever I try to change the SNN from a Point IO Im missing the three ... dots to open the pop up and change it...
636
I created a new project with a 1756-L72S controller. Now I want to change the controller but the option to change the controller is grayed out...
4,695
Hi all Was wondering if you guys were able to help. I am onsite trying to program a 440C-CR30-22BBB Safety relay. Using the following pdf and...
4,442
Hello everyone, I'm new here, I hope someone can help me. I've been trying to install EDS files to my Studio 5000 with the EDS tool installer but...
118
Hi Everyone, I am facing an issue while installing the STUDIO 5000 in my windows 10 PC. During installation I am getting an error that " Error...
186