I am trying to convert a program from S5 to S7 and having a few problems.
I have managed to produce source code and open it within Step7. The problem is when I perform a consistency check I get lots of errors (more than 100). The message I get is -
'Transpositions in the order of parameters at XXXX can result in transpositions/shifts in comments even in the subsequent statements.' (XXXX varies depending on the variable)
I initially thought that the problem occured when a WORD data type was loaded with the data B#(106,5) but now I am not so sure.
Can anyone help?
Cheers
Mike
Here's some code that compiles with the error you are getting. As you can see I have swapped the order of the parameters when calling FC1. I suspect a similar situation with your code.
How sure are you of the integrity of the Step 5 project ?
Code:
FUNCTION FC 1 : VOID
TITLE =
VERSION : 0.1
VAR_INPUT
Step : BOOL ;
Step1: bool ;
END_VAR
BEGIN
NETWORK
TITLE =
END_FUNCTION
FUNCTION FC 2 : VOID
TITLE =
VERSION : 0.1
VAR_INPUT
Step : BOOL ;
END_VAR
BEGIN
NETWORK
TITLE =
call fc1(Step1:=m0.0,Step:=m0.0);
END_FUNCTION
What a hero!
I have changed the order of the some of the parameters to match the order within the function and the errors have disappeared
It would seem that the S5 - S7 conversion process doesnt take account of the order of the declarations in the function.
Thanks for your help.
Mike
I have managed to make all the IO for the conversion to work. the problem is the rs232. the machine I am installing this on give me a EM50...
2,803
I can't seem to get the Panel View Plus 7 standard edition to downgrade to V_11, when I check the AB downloads and compatibility websites for this...
137
Hi I used to be able to launch PLCsim without any problem. Now it tells me " STEP 7 Professional Licence is required to simulate this PLC"...
533
Hello! When trying to load the hardware configuration I get error 0050-133 2 2458, check the diagnostic buffer. When checking the buffer, it says...
187