My company is building a machine that has a HMI that uses FTview SE Network distributed system.
the HMI server and network directory are located on a computer that is located within the local PLC network (192.168.125.XXX) and the local PLC network is connected to a router that connects our system to a larger ethernet (I´ve been using 192.168.1.XXX for testing)
So the client requires a computer that is connected to the 192.168.1.XXX larger ethernet network to display the HMI interface for our machine and this is what I am trying to set up... but I am unable to specify the network directory to the location of the computer within the local PLC network because I am unable to find it when I open "specify factorytalk network directory location"
Is this possible to have a FTview client on a seperate network connect to a FTview server and network directory that is on another netowork ?
Any help and/or suggestions regarding how to achieve this are greatly appreciated :)
see simplified network here:
https://postimg.org/image/x1hwz64qr/
Best regards,
Steinar
Thanks Garry,
The subnetmask for both networks is 255.255.255.0, The router on that connects to the larger network is configured as a DHCP client.
I think my solution is to have two ethernet cards in the HMI server computer that hosts the network directory... and have that configured as DHCP client, that way I should be able to see the computer that hosts the network directory on the larger network (192.168.1.XXX) ... that will atleast be my next try :)
Regars,
Steinar
Yes, this is possible, and you shouldn't need any extra ethernet adaptors.
I have a network distributed FTView SE application running almost exactly as you describe:
FTDirectory on 192.168.1.xxx (main corporate network)
HMI servers on 192.168.10.xxx (central process network)
Clients on different subnets according to production lines (192.168.11.xxx, 192.168.12.xxx, 192.168.13.xxx and so on)
It all works perfectly. Of course, you have to have routing set up correctly between all networks, and all of the devices need to have the correct gateway address set.
It was too long ago that I set it up, so I can't remember exactly how I did it, but if I recall rightly, the only problem that I had was that you have to specify the directory by NAME, not by IP ADDRESS. As you have to use the Fully Qualified Domain Name (FQDN), you have to keep the PC name under 15 characters.
Hope some of that helps!
Coverting a Factory Talk Local project t a network distributed project
Good afternoon members. I am new to this forum and a beginner when it comes to FT. I have an issue where a client would like to convert their local project to a network distributed project. Is there anyway this can be done?
I've posted this on the ptc forum as well, but no luck with an answer (waiting for my service contract number) I keep getting the following error...
163
I have a fresh out of the box 5069-L306ER connected to power only. I am unable to set the IP address of the plc through USB OR ethernet using RS...
18
7,473
for some reason when i try to change the value for the preset on a rto timer after i change it accept changes it goes back to the old value, any...
2,209
I have SIMATIC S7 v5.4 sp4 when I tried to display cross reference table it gives the message [internal error: unable to set up the connection...
3,074
Recently we have purchased the Rosemount 752 remote indicator to replace with new one, Capability file for that FF Device is unable to import with...
46