Hi all. I’ve got an FX1n running a P/I loop. When the output of the loop is required to drive full-on, the value in the associated register counts up and eventually exceeds the advertised range of 32767 and continues onward, which means that the 16th bit in that register comes on and the output is interpreted as negative. This doesn’t help much in maintaining the real output in a saturated state. Any thoughts or experience on this one? Cheers.
Thanks, Shooter. I understood what was happening, but not why it was happening, especially as the manual gives a range of 0 to 32767 for the output. Can I specify a "D" register to be unsigned? DB.
I've never done PID control on a FX1n but are there not minimum and maximum control limits built into the PID instruction? There should be some way of controlling the PID output and limiting it to a certain range (I'm thinking a combustion air system where you never want to fully close the air/gas valves)
Even if its not in the PID instruction itself, could you not put [Less than] and [greater than] instructions ofter the PID to limit its output?
PID overflow is inexcusable
The PID should never overflow. It should saturate at 32767 and stay there. Limiting the output will not limit the control signal generated by the PID. It will still take time for the PID to unwind a get back into the positive range.
I would write my own PID but first I would find out why the control signal needs to saturate. This is caused by a few things:
1. The polarity of the wiring is wrong. If so there will be positive feedback instead of negative feed back
2. The control system doesn't have enough power to reach the set point.
3. A step change in the set point is causing a huge error and the resulting huge control signal.
Christoff, that's exactly what I had to do. Effectively: if [o/p] >32767, [o/p]=0. I really didn't want to for the reason that Peter states. Peter, the wiring is ok; there's enough power to do the job (when it settles, it's running at about 30%). But from cold, or even a large positive demand step change, surely there's nothing wrong with it saturating so long as the proprietary loop software doesn't do crazy things like exceed the advertised max value? DB.
Hi, I'm currently having issued with a PowerFlex 252. It was working fine last week, and suddenly decided to stop working. When I go into...
121
[Update: fixed a typo in the image.] See the image below, especially the blue-ish annotations. The three rungs ending in output coils -( ) are...
17
1,009
Hi all, I've run into an error I haven't seen before while attempting to download the “Programming” tab of RMCTools to an RMC200 Lite I just got...
3,694
First, a background on the equipment so you know what is going on. I have an AB ControlLogix L63 processor controlling some Mitsubishi...
17
6,031
Hi, I'm getting a bunch of these warnings when I build the program in Connected Components Workbench. The program is legacy code. The program...
2,408