Using EDS file to configure message
Fr-Felipe
Sep 2016
SC
I`m trying to command a Mitsubishi inverter F800 using a Micrologix PLC with message instructions.
I sucessfully controled it using a Compact Logix with a EDS file.
Opening the EDS file i have these information:
[Params]
Param1 =
0, $ reserved, shall equal 0
6,"20 29 24 01 30 03", $ Link Path Size, Link Path
0x0000, $ Descriptor
0xC1, $ Data Type
1, $ Data Size in bytes
"Run forward", $ name
"", $ units
"Run forward", $ help string
0,1,0, $ min, max, default data values
,,,, $ mult, div, base, offset scaling
,,,, $ mult, div, base, offset links
0; $ decimal places
Is possible to decode the "link path" to send information using message or another instruction ?
Welcome to the Forum !
When you say you "controlled" the F800 with the CompactLogix, do you mean you put it into the I/O tree and used the cyclic I/O connection ?
While it's possible to send CIP Generic messages using the MicroLogix 1100 or 1400 controllers, it is likewise very strongly recommended AGAINST to use that method to control a variable-frequency drive.
The MicroLogix simply isn't designed or built to do control over an Ethernet network. It doesn't have the cyclic I/O connection capability or a dedicated daughtercard to handle those functions.
If you're going to do the stop/start control over hardwire and use messaging to retrieve status data or occasionally send a configuration parameter, my stance softens somewhat.
Hi Ken, thank you for the warm wellcome !
Exactly, i controled the F800 with cyclic I/O connection.
And stop/start will be controled using hardwire, but i need to change speed occassionally.
I can read and write parameters to the inverter, but i can't change the frequency sucessfully, in that point enters the EDS file, i want to look where this value is being written.
You are correct that the EDS file provides clues to the DeviceNet module objects supported by the device.
Can you post a link to the EDS file you are using for this drive ? I could not find one with a brief search of the Mitsubishi website.
Question – I am running the RSLinx Classic Gateway OPC server (4.00.01 CPR 9 SR 10.0) on my laptop, with a directly connected Ethernet/IP...
2,625
I just installed a system using a 9300-ENA network device. The uplink port is connected to the plant network and the local to a L30ER compact...
8,628
I have two computers using the same version of RSlinx. I also downloaded the EDS files from Turck to read the I/O. I registered the .eds files...
3,858
Hello. I am new to S7 programming and need some help. I hope I´m clear enough... I need to read some data(current,power,...) from a SENTRON...
5,951
I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
64