Looking for some OEM or Industry guidance, due to mechanical damage some of our drive cables have been compromised. (Document to reference would be great)

Our contractor in a Shipyard have asked if they can SPICE some VDF Cables ( Between Motor and VDF) rather than pull in a new conductor. These are Medium Voltage large KW drives, 100/200KW with long 60~70m runs.]

I guess this request has come as a cost saving request?


Marine Application for ship
 
Yes you can.
We have a terminal box where we transition from regular screened cable to highly flexible screened cable.
Anything that changes the impedance slightly will be a source of reflections, i.e. more noise, but we do it and don't have problems with it.
 
I guess this request has come as a cost saving request?

Time and money I'd imagine. That cable could potentially be 120sqmm, that's got to be what, £50 per meter?
It's going to be a day or two of work for several people to install a full new cable.
 
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline

JesperMP's Avatar

Join Date: Feb 2003
Location: ᚴᚬᛒᛅᚾᚼᚬᚠᚾ
Posts: 15,980
I assumed that the question was for a screened cable between a VFD and a motor.
But now I think that by "VDF" maybe you mean something else.
__________________
Jesper
NOTICE:
JesperMP has passive-aggressive tendencies, can be impolite and may even use sarcasm !

No your correct the Cable between the Motor and the Variable Speed Drive
 
When you take a VFD cable via a motor isolator you do essentially the same thing. You'd use an isolator with VSD glands that keep the screen continuous.

If it was me, and there was space to do so, I would use a ferrous junction box and VSD brush glands. Joint cables internally using crimp connectors.

If there's no space, then joint the normal way. Use a foil wrap to replace the screen, seal overall using thickwall glued heatshrink.
 

Similar Topics

Hello everyone I'm new on this forum... And I think that have a big problem with a PF 700 I'm a working in a food plant, this weekend was...
Replies
7
Views
2,216
Hi, I was noticing that Profibus connectors have 2 ports on them that can house 2 separate cables. Can I use 2 cables with Profibus signals...
Replies
4
Views
228
Can anyone recommend a flexible 600-volt shielded ethernet patch cable? I have used them from Allen Bradley / Panduit before and they are too...
Replies
0
Views
124
Hi all, i have several Proface GT2400 terminals and i need to get the software and interface cables and i have several questions. I am assuming...
Replies
3
Views
184
Hi all, I wonder what's the best type of cable to use for RS-485 2 wire + GND That is, Data+, Data- & GND I know that Belden 9841 (not...
Replies
10
Views
1,134
Back
Top Bottom