I would think that if one thought of the "HI" warning as just as important, the "HI-HI" would be a little less critical. Redundant sensors may be a good approach also.
There is one of these systems on Lake Michigan, near Ludington, MI. I have been in the pump room on business but not involved with level control. Very interesting system.
As seems to be the case so often, the failure was the result of multiple errors and misjudgments in design, construction and operation. The reservoir did in fact have redundant sensors, but the backup sensors (conductivity probes) ended up being above the overflow elevation of the parapet wall! And the primary (pressure) sensors were reading low because they had come loose from their mountings.
This would make an excellent case study for a class, because the basic problem is so simple. And the report touches on an interesting question for discussion: the fact that the control system could have been programmed to identify abnormal conditions - without any additional hardware - by comparing water depth readings with expected values based on pump runtime.
I actually refused to put HI-HI alarms in circuits at the water plant, against designer wishes. If a high-level alarm occurs, tend to it! Adding HI-HI does just what Russ suggests - causes an apathetic approach to high level alarms.
I would differentiate between add a Hi-Hi failsafe switch vs not adding a Hi-Hi alarm. For mission critical situations never rely on a single device. Have either device set of a single Hi alarm if you wish, but it'd be foolish not to install a secondary switch. I refuse to guarantee tank operations without failsafe backup devices and always push the customer hard to install them. I shake my head when I see a tank on load cells or a continuous level probe with no discrete high level failsafe switch.
Hello everyone Iam working on washing machine which washing onion and water level is very critical for the process. The machine used IFM 121 for...
145
dear, i am assigning start/stop levels for the sump pump, i was wondering what is the minimum differential level that can be used when a float...
2,604
Dear all, i have LS1200 murphy used for suction scrubber (connected NC contacts to 1756-IQ16 card) and the question is: when i triggered switch...
1,742
Hi Guys, I wrote a Program on Tank Over fill Protection system. There are Five Tanks/Five Rosemount 2120 Level switch inputs and One Audio...
1,588
Dear, I am trying to size level switch contact rating for a specific application. we will be using multilin 469 as below...
1,897