WE HAVE HAD A DIRECT LOGIC 205- DL250-1 PLC FOR 8 YEARS. NO PROBLEMS. LAST WEEK WE HAD A SHUTDOWN AND AFTER WE TURNED POWER BACK ON WE HAVE NOTICED OUR ANALOG INPUT AND OUTPUT (4-20Ma) SIGNALS ARE AROUND 50% HIGHER THAN USUAL. THE 24V POWER SUPPLY HASNT CHANGED,STILL STEADY AT 24V.
THE CARDS ARE FD-O8AD-1/FD-08DA-1 . NEITHER CAN BE CALIBRATED. DO YOU THINK WE HAVE A BAD PROCESSOR?
 
Hello,

Is the A/O that is wrong Dependent on the A/I that is wrong?

Have you checked the actual mA reading coming into the input to see if it is what you expect it to be or if it is 50% higher than what you would expect it to be?
 
Both the input and output signal are independent of each other. We are going to check the counts tomorrow. Its very strange both cards are reading high . I am sure its the processor ?
 
AFTER WE TURNED POWER BACK ON WE HAVE NOTICED OUR ANALOG INPUT AND OUTPUT (4-20Ma) SIGNALS ARE AROUND 50% HIGHER THAN USUAL.
You don't say what the field sensors are. It would be highly unusual for multiple field sensors to fail in the same fashion simultaneously. But they could be reporting the truth depending on what the app is. For instance, if they're pH in an equalizing batch tank, the contents might very well have doubled in pH after an outage.

THE 24V POWER SUPPLY HASNT CHANGED,STILL STEADY AT 24V.
4-20mA field devices are current regulators so a higher than normal (but still within tolerance) power supply voltage will be compensated for by the field device(s). A power supply lower than required will result in a failure to drive the loop load resistance, appearing as a failure achieve a 17 or 18 or 19 or 20 mA value, depending on what the loop resistance is and what the power supply voltage is. So it's not the power supply.

THE CARDS ARE FD-O8AD-1/FD-08DA-1 . NEITHER CAN BE CALIBRATED. DO YOU THINK WE HAVE A BAD PROCESSOR?
Usually the AI card converts the analog signal to a digital word format that the CPU uses. So the first suspicious component is the AI card. I'd replace the AI card before replacing the CPU.

Let us know what you find.
 

Similar Topics

Hello, I have an automation direct d2 262 plc and C-more HMI EA9T6CL-R. I need to prepare a program, scheduled to be performed on a future date. I...
Replies
1
Views
119
Hello all- I have a unique challenge using a customers Direct logic 06 PLC. This customer has a DC motor operating at 10 RPM which is turning a...
Replies
1
Views
136
Hi, I have been trying to run drive via Sysmac studio. I can ping the drive. I can see the logic bits going on/off as per command. But, drive is...
Replies
21
Views
565
Anyone tried Automation Directs new CM5 HMI. We've been the EA9's for a few years now with minimal complaints. A few failures here and there but...
Replies
17
Views
1,588
I'm using an Automation Direct GS20 VFD for the first time and I have a question for the Automation Direct gurus regarding the recommendation of a...
Replies
2
Views
1,100
Back
Top Bottom