I know the 1794-AENT is a 24 vdc option for flex ethernet when adding a flex rack to controllogix. Is there a 120 vac option for the 1794 Ethernet standard?
We are upgrading a Micrologix 1000 to Flex IO and only have 120 vac in the cabinet and if possible I dont want to install a transformer for just one item needing 24 vdc.
 
Ah... so it takes in 120 vac and converts to 24 vdc for the ethernet flex? I didnt know that...

Thank you.
 