Have a Red Lion G306k000 screen which displays the MAC address, how can I determine an IP address to which I can download some code from Crimson 3.

It has been reset hence the display

" INVALID DATABASE.

IP address not configured and TCP/IP is disabled.

MAC Address is 00-0C-26-02-47-40."

Have tried via RS232 but no joy as yet.
 
The G306K was discontinued some time ago and replaced by the G307K2.

I'm not certain but I think the only way to enable the Ethernet port is to first download a program through the RS232 port. Your initial program should configure the Ethernet settings and enable remote download, and at that point you can use Ethernet for programming.

Another thing to keep in mind is that the Crimson build on your PC must match the firmware in the unit. If it doesn't, then when you go to download your program it will first update the firmware. Over RS232 this is no problem but over Ethernet you must have a CompactFlash card installed for this to work. (Another reason to have serial programming capability.) I don't believe you can use a normal null modem cable to connect to the programming port, so you have to either buy Red Lion's cable or make your own. And unless your PC is ancient and has built-in serial ports, you'll also need a USB-to-serial converter.
 
OK Thanks I will investigate the cable route, it is a rather old piece of kit and I inherited the project from a client who told me an "electrician" had tried to make some changes to the plant but succeeded in wiping the database and the PLC code as well..Doh!
I always end up with these type of problems.
 

Similar Topics

While they came up quickly with a fix for the alarm date issue quickly I will have to drive around for a week or so, burning up a lot of fuel...
Replies
4
Views
266
From the Red Lion website, after some customer enquiries in the last week or so... Rev. March 25, 2024 [18:30] Just thought it might help a...
Replies
9
Views
279
How do you install update on Red Lion Crimson ver 3.1. Do I just need to run the exe file on the host server?
Replies
1
Views
107
Hello All, I need the ability to remotely reboot a Red Lion CR3000 HMI. Due to some graphics issues when the database is updated the HMI must be...
Replies
4
Views
220
I'm trying to use a Red Lion Cub counter (Cub5B00) as a counter and give the cub's counts to a Graphite G12 PLC/HMI to display. After about an...
Replies
1
Views
111
Back
Top Bottom