View Full Version : Factory Talk View Studio, DH+ Tags


mykeeplace
September 9th, 2016, 12:15 PM
I am setting up to use DH+, to a PLC5, but having trouble where the tag set ups.
I can see the processor in the comm set up. But having problem writhing a tag that works. Like I setup a comm [PLC5] and want to display value in N7:10 integer file on a counter display. have {[PLC5]N7:10}, but when I go to running man, no luck in seeing the display number.

dmroeder
September 9th, 2016, 12:20 PM
I looked at an application that I did many years ago and the format was like this:

{::[PLC5]N7:10}

I think you need the "::" in there.

mykeeplace
September 9th, 2016, 06:03 PM
Look though the classroom books. Manuals, and shop programs, here. Was getting ready to build a 1000e panel-view and then convert it to panel-view plus.

Thank you very much.

:bow:

Mike