Hello fellas... Been a long time.
I'm currently stumped. O:6/8 comes true (on) at every power cycle. For the life of me I can't figure out why. I power up and O:6/8 turns on. I toggle bit to "off" and we good to go, however if power is recycled O:6/8 turns back on.
O:6/8 is only referenced in three locations, once each as OTU, OTL and XIC. Both the OTU and OTL require real world inputs to be present to change. We have all input wires disconnected so there is zero chance that the inputs are seeing a blip on at shutdown. I swapped output cards with same result so its not the card.
It looks like this: (attached)
I'm currently stumped. O:6/8 comes true (on) at every power cycle. For the life of me I can't figure out why. I power up and O:6/8 turns on. I toggle bit to "off" and we good to go, however if power is recycled O:6/8 turns back on.
O:6/8 is only referenced in three locations, once each as OTU, OTL and XIC. Both the OTU and OTL require real world inputs to be present to change. We have all input wires disconnected so there is zero chance that the inputs are seeing a blip on at shutdown. I swapped output cards with same result so its not the card.
It looks like this: (attached)